    National Electric Code for underground wire
    Does underground wire for street lighting have to be covered?
    Clough's Avatar
    Clough Posts: 26,677, Reputation: 1649
    Uber Member
     
    #2

    Jan 21, 2010, 02:50 PM
    Hi, semichael!

    If the wire is supposed to be underground, then yes, it would need to be covered.

    If it's installed according to a local code, that may be another issue.

    What are specific reasons that you're asking the question, please?

    Thanks!
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Jan 21, 2010, 02:53 PM

    What do you mean by covered?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Jan 21, 2010, 02:56 PM
    If you mean that is wire allowed to be laid on the surface of the ground for street lights, I don't think so.

    Imagine all wiring to all street lights were laying on the ground. People would be tripping all over.
    semichael's Avatar
    semichael Posts: 2, Reputation: 1
    New Member
     
    #5

    Jan 21, 2010, 02:59 PM
    Quote Originally Posted by Clough View Post
    Hi, semichael!

    If the wire is supposed to be underground, then yes, it would need to be covered.

    If it's installed according to a local code, that may be another issue.

    What are specific reasons that you're asking the question, please?

    Thanks!
    Two of our street lights went out. An electrician said the wires were installed without conduit and were bare. The NEC requires type UF at a minimum. Local ordinances only apply if they are stricter than the NEC of NFPA.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Jan 21, 2010, 03:02 PM
    OK now we are getting somewhere.

    There are types of insulation rated for direct burial, do not need to be installed in conduit.

    One popular insulation is USE, and are individual conductors.

    Perhaps the electrician should check the type of insulation.

    UF is a cable assembly containing more than one conductor.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #7

    Jan 21, 2010, 04:27 PM

    I have also seen UF in individual conductors.

    Other than that, what TK said. I have seen plenty of parking lots with direct burial cable. Dumb idea in the long run though.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

National electric code free online [ 6 Answers ]

I need to install a lit exit sign in a 759 sq ft. office. The door that I am putting this unit above is located far from the other already installed exit sign and would require going through a block wall at an added expense to the customer. Will the code allow me to connect the sign to an...

National electric code free online [ 16 Answers ]

What's the distance for gfci from water fixture?

National electric code free online [ 2 Answers ]

Outdoor uplighting requirements for low voltage and 120v?

Reading the NFPA 70 etc. National Electric Code Online [ 1 Answers ]

It does seem impossible to search for, but just about any code published by the NFPA is readable online. You will have to register for a username and password. The NFPA 70: National Electrical Code starts here: NFPA 70: National Electrical CodeŽ Near the bottom af the page there is a...


View more questions Search