    I purchased a 120v walll heater for my bathroom. I also purchased the optional wall mounted double pole thermostat from the same vendor. I have wired many home projects but I never worked on a double pole device. The power supply I want to tap into also feeds the motor to the bathroom hot tub. The tub motor is rated at 120v 20 amp. With what appears to be a 10 gauge romex power source and is dedicated at the circuit breaker. The heater is factory wired to draw a maximum 1500w and 12.5A. With one power line how do I wire the thermostat and wall heater (heater and thermostat both have two red and two black wires and a ground)?
    14u2c's Avatar
    14u2c Posts: 34, Reputation: 1
    Junior Member
     
    #2

    Jan 18, 2010, 01:01 PM

    I would run a new circuit for the heater cause the hot tub probably is on a gfi if you try to break of it.. it would probably wind up tripping it..
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Jan 18, 2010, 01:18 PM

    A) You did not need or want a double-pole thermostat. You need a single-pole.

    B) As 14u2c states, DO NOT use the feed to the tub. This most likely is required to be a dedicated circuit and tapping into it would 1) be a violation, and 2) not be smart because you would NOT be able to use both items at the same time.

    Run a new circuit.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #4

    Jan 18, 2010, 02:34 PM

    Can't he use the double pole thermostat, and parallel the contacts to reduce the load of one set, or just use 1 set of poles?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #5

    Jan 18, 2010, 03:50 PM

    He sure could. I would just use one set as opposed to paralleling them.
    I guess the cost difference between the two would not make sense to go exchange it. :o
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Jan 19, 2010, 06:13 AM

    The thing to remember with many two pole thermostats, is one pole is only a switch, closes as soon as the stat is turned from "OFF" to a higher temp setting. The other pole has the actual thermal sensing action, will close when temp falls.

    If only the temperature sensing pole is used, it is never a positive open when OFF is needed, can close anytime as temp falls.

    A single pole stat is needed when used for a 120 volt device.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring Hot Tub and using a 50 Amp Double Pole GFCI Circiut Breaker [ 10 Answers ]

:confused: I keep getting the GFCI breaker tripping after wiring my hot tub. I wired 2 hot Red and Black to the proper terminals and the White to the neutral and the Bare Copper to the ground Post at the tub. I am using 6-3 w/G per instructions. Could the GFCI breaker be bad? When I wire...

Wiring single pole thermostat in double pole fixture [ 3 Answers ]

Hello, I am trying to install a line voltage programmable thermostat into a manual thermostat fixture. The programmable thermostat is Honeywell RLV430. Instruction manual here: http://www.homedepot.ca/wcsstore/HomeDepotCanada/images/catalog/b7867367-6c05-4c82-a97c-648044b91564.pdf The...

From double pole to single pole thermostat -2 extra leads [ 3 Answers ]

The double pole thermostat for the baseboard heater has a red and a black wire coming in (from the circuit panel) and a red and a black going to the heater. The new single pole only has a red LINE lead and a black LOAD lead. If I attach red to red and then black to black, I have black (from...

Two Single Pole GFI's = one Double Pole 220v GFI? [ 6 Answers ]

Hello there, Installing a pool motor, 220v hayward northstar two speed. Could not find a double pole 40 amp GFI, electric supply store recommended two single pole 20A GFI's sharing a neutral? Does this make sense. I have a 40amp double pole in the main feeding the sub via the sub panel...


View more questions Search