    Justin002's Avatar
    Justin002 Posts: 2, Reputation: 1
    New Member
     
    #1

    Jan 14, 2010, 07:55 PM
    My Goodman GMPN060-3 Rev A tries to start up but hums for about 4 minutes and stops.
    My Goodman GMPN060-3 Rev A tries to start up and hums for about 4 minutes and stops. There is a solid red light. I've reset it and turned everything on and off I can see. I came home around 7 and have been tinkering w/ it. Nothing seems to get it to go. Anyone outhere that can help at this time would be much appreciated.

    Thanks.
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #2

    Jan 14, 2010, 08:08 PM

    This is a condensing furnace(makes water when it heats) You can have a froze or restricted drain line going to the outside tripping the pressure switch. You should have a flashing light on the control board letting you know what's wrong.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #3

    Jan 14, 2010, 08:10 PM
    http://www.alltemp-hvac.com/gmpn.pdf

    Your manual.

    What is humming?
    Justin002's Avatar
    Justin002 Posts: 2, Reputation: 1
    New Member
     
    #4

    Jan 14, 2010, 09:19 PM

    Thanks guys, but just gave up for tonight and just took the family to a hotel. Just checked in @ the Super 8 in town. Free WiFi. Anyway, will try to tinker with it tomorrow. Thanks again. The light on the unit was solid red. The humming sounds normal , maybe used the wrong word. It sounds like it's going to start like normal but fails after a few minutes. I tested the fan on fan only and also tested the AC unit. It seems to work fine in both instances; however, just the heating it tries to kick on but fails to ignite and the fan does not start on the heat mode. Thanks again.
    Justin Orr's Avatar
    Justin Orr Posts: 24, Reputation: 1
    New Member
     
    #5

    Jan 14, 2010, 10:21 PM
    Well the fan not starting in heat mode is a problem because it runs before the ignitor ignites the burner. It needs to blow the stagnant air out before the burners ignite as an added safety precaution. If the fan doesn't turn on at first, the vent pressure switch won't close, and the heat circuit won't energize at all. So why won't the fan turn on? Its got to be a low voltage problem within the heat circuit because it operates when you turn on "fan on". My guess is it could be either the power vent relay or the fan blower relay 2. when you hear this humming, does any air blow out of your vents? Do you feel any warmth at all? There are many safety switches that can trip for many reasons, so my guess is its one of those. The problem is finding which one. If it's the fan blower relay number 2 (referring to the schematics in the manual that hvac1000 provided, last page) then the humming could be the first fan used to purge the ductwork. Then the burners ignite and when the first fan shuts off and the blower fan is supposed to take over, it doesn't, causing safety switches to open up and extinguish the flame before anything can start. Just a theory.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Goodman GMPN060-3 (5 Blink Diagnostic Code) [ 4 Answers ]

Hi, I have a Goodman GMPN060-3 gas furnace. I get a 5 blink diag code, the indoor blower comes on. It worked OK for 3 hours this morning, I had to have the board replaced back Nov 04, I am wondering if it is going bad again, I am on disablity with limited income, any help will be gratefully...

Goodman Furnace Model GMPN060-3 Three Blinks Diagnostics. [ 7 Answers ]

I have a Goodman Furnace Model GMPN060-3. I get three blinks biagnostic code. I changed venter (motor assembly) and pressure switch. Still the same three blinks. Moisture drain path is clean and free of debries. After the new parts, furnace started once, but would not start again -- same three...

Goodman gmp 075=3 rev b dead [ 13 Answers ]

Jumped the thermostat, blower doesn't start, no flame, heard a click from the furnace when turning up tstat. Fuse on board was blown, replaced. Followed lighting instructions to no avail. Help please its getting chilly...

Goodman GMPN060-3 Blower Cycles [ 2 Answers ]

I have been in my house for 5 years when the thermostat calls for heat, the inducer blower comes on and almost immediately I hear the pressure switch click and then the relay on the main board clicks and the inducer blower goes off. This happens over and over for a couple of minutes and finally...


View more questions Search