New Member
|
|
Jan 6, 2010, 04:57 PM
|
|
Multiwire branch
I've got a multiwire branch circuit that I believe is wired improperly. From what I understand these circuits can be dangerous if wired with both hot conductors on the same pole (same side of the panel). Am I correct to say that they should be wired on opposite sides of the panel? Can I take one of the hots and extend it to the proper side of the box with a pigtail, or do I actually have to pull a longer length of wire to get it there (very difficult at this stage in the game). This is a 100 amp service that supplies a 425 square foot apartment in the upper level of a house so the panel is not crowded by any means.
|
|
 |
Uber Member
|
|
Jan 6, 2010, 05:32 PM
|
|
Next to each other is best and on a 2 pole 20 amp(if #12)breaker.
They need to be on Opposite phases.
240 volt circuits uses each phase.
If both are on the same phase neutral current can go as high as 40 amps and heat/burn up.
You can verify you are on opposite phases by measuring the 240 volts if wired correctly.
If you were measuring across the same phase, the voltage would be zero.
|
|
 |
New Member
|
|
Jan 6, 2010, 06:22 PM
|
|
Don't circuits wired with 14 gauge wire need to be on a 15A breaker max?
|
|
 |
Uber Member
|
|
Jan 6, 2010, 07:36 PM
|
|
Yes, you didn't say, and I said 20 Amps(if #12).
It would be 15 amp 2 pole breaker for #14.
|
|
 |
New Member
|
|
Jan 6, 2010, 08:31 PM
|
|
Sorry, missed the parentheses. This makes sense to me now. Thanks for your help!
|
|
 |
Uber Member
|
|
Jan 6, 2010, 08:33 PM
|
|
Good Deal. Anytime
|
|
 |
Ultra Member
|
|
Jan 6, 2010, 08:35 PM
|
|
Any chance you have a Federal Pacific panel?
|
|
 |
New Member
|
|
Jan 6, 2010, 09:22 PM
|
|
Square D QO.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Cherry blossom branch
[ 1 Answers ]
May I ask where the cherry blossom branch tattoo was done? It is beautiful!! What is the name of the artist? Just
Which branch in m.tech suits for me
[ 1 Answers ]
I completed b.tech in ece(jntu).I want to do m.tech.among vlsi design,embedded,digitalelectronics,which is best for me to build my carrier?
Mutiwire branch Circuts
[ 10 Answers ]
I noticed a while back that I have 2 14 AWG multi-wire branch circuits from my box. Although they are not connected to dual breakers. Is this okay as long as they are connected to opposite legs on the service panel? I know if they were on the same it would be a big no no. Also I noticed that one of...
View more questions
Search
|