Jan 3, 2010, 11:08 AM
|
|
My furnace won't stay on
I have a three year old bryant 340aav furnace. It starts and the burner lights. It runs for about 15-20 minutes and then shuts down. There is a red code light that flashes an error of 13 or 33.
|
|
 |
Heating & Air Conditioning Expert
|
|
Jan 3, 2010, 11:19 AM
|
|
Read the label on the back side of the blower motor access door to find out what the blink/flash code means then refer to the link below for part locations.
http://www.bobsheating.com/PDF/Plus-...owners-man.pdf
|
|
 |
New Member
|
|
Jan 3, 2010, 11:26 AM
|
|
Thanks anyway. I did that already and am still stuck. It is either a code 31 or 13. Anything else you could recommend?
|
|
 |
Heating & Air Conditioning Expert
|
|
Jan 3, 2010, 12:07 PM
|
|
Yes post the meanings for the codes you mentioned for your specific furnace.
|
|
 |
New Member
|
|
Jan 3, 2010, 12:42 PM
|
|
Code 31 pressure switch did not close or reopen. I turned funace off and then on. It starts and runs and then shuts off. There are three rapid flashes followed by one long red flash.
|
|
 |
Heating & Air Conditioning Expert
|
|
Jan 3, 2010, 01:32 PM
|
|
You might take off the hose connection and make sure it is clear with no restrictions or cracks/damage
|
|
 |
New Member
|
|
Jan 3, 2010, 01:39 PM
|
|
Which hose connection? Thanks.
|
|
 |
Heating & Air Conditioning Expert
|
|
Jan 3, 2010, 01:41 PM
|
|
The ones that go to the switch
|
|
 |
New Member
|
|
Jan 3, 2010, 01:54 PM
|
|
Can you please give me a little more detail on this? Thanks.
|
|
 |
Heating & Air Conditioning Expert
|
|
Jan 3, 2010, 01:56 PM
|
|
The pressure switch is connected by a small hose. This hose if defective or plugged up can cause problems. If you cannot find the hose I do not know what else to say. Sorry but you might be better getting ON SITE service for your unit.
|
|
 |
New Member
|
|
Jan 3, 2010, 02:27 PM
|
|
I found the hose it has a pink tag on it and the switch. I disconected it from the switch and plate that runs into the furnace. The tube is clear and I can blow through it. When I disconected it from the side that goes into the furnace a steady flow of water came out. I have my furnace in the upright position.
|
|
 |
New Member
|
|
Jan 3, 2010, 02:33 PM
|
|
I found the pressure switch and hose. The hose is clear and in good condition. When I removed it from both ends a little stream of water backflowed into unit from the black plate mounted to the furnace not the switch end. Is that water normal?
|
|
 |
Heating & Air Conditioning Expert
|
|
Jan 3, 2010, 03:56 PM
|
|
Have you tried to start the furnace since you cleared the tube?
|
|
 |
New Member
|
|
Jan 3, 2010, 04:11 PM
|
|
Yes. Same issue. I just removed the swith and I gently tapped it on my leg. I am going to hook that up again and try it?
|
|
 |
New Member
|
|
Jan 3, 2010, 05:16 PM
|
|
Still nothing. Same thing time and time again. Runs for 10-15 minutes, then flame goes out and blower continues to run. At leat its only going to be 15 degrees tonight. Called several heating and cooling places and I am awaiting a return call.
|
|
 |
Plumbing Expert
|
|
Jan 3, 2010, 06:35 PM
|
|
There should not be any water coming out of pressure switch hose(where hose connects to heat exchanger). This is a sign that the drain system on your furnace is clogged. Disconnect and clean all drain hoses and all ports that drain hoses hook to. As your furnace runs, it condensates and the condensate needs to drain off or the water will just back up in the heat exchanger and or exhaust fan causing the pressure switch to open during operation. The reason it starts back up is because the water is slowly draining(not fast enough due to a partial clogg somewhere in the drain system) So when you shut the heater off, the water slowly drains, then when furnace is kicked back on, the water is building up faster than it can drain, so the pressure switch opens, and the furnace shuts down. Just clean all rubber hoses and all ports and traps that they may hook to. The water has to drain to somewhere, so follow the drain pipe on the outside of the furnace and make sure is it clear of cloggs and can drain easily. Hope this helps.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Goodman GMP100-3 Furnace won't Stay On.
[ 14 Answers ]
Hello,
I have a Goodman Furnace (model # GMP100-3). The furnace will not stay running. Here is the sequence of events for two different scenarios that are occurring.
Scenario 1
1. Thermostat Calls for Heat
2. Inducer starts
3. Pressure switch closes
4. Heating element glows
5. Burners...
Furnace won't stay on
[ 1 Answers ]
Rheem criterion RGDG, changed the board this summer to fix blower, the glow stick comes on, the gas lights in all chambers. The gas stays on for several seconds then shuts off. I have three LED's the two on the right are green and stay lit, except for the middle on which starts to blink after the...
Goodman furnace won't stay lit
[ 1 Answers ]
I have a goodman furnace that goes like this.
Inducer fan comes on, 10 secs later glow lights up,
10 secs later get blue flames
10 secs later blue flames goes out. Repeats 3 times
I have replaced the flame sensor still same problem
But here is the thing. I am only getting 10 volts to the...
Furnace won't stay on
[ 4 Answers ]
I have a gas pump furnace that has been switched over to propane prior to me moving in.
Replaced filters and thermostat, checked all fuses and junction box. a/c works and fan only works but when I turn it to heat - I get nothing. I removed panel and reset the switch - it stayed on for about 3-4...
Furnace Blower won't stay on
[ 1 Answers ]
I have a problem with my furnace blower not staying on. I can set my thermostat for say 74 degrees and the furnace will come on normally. I can hear and see the furnace on, but it takes roughly one minute (ive timed it) before the blower comes on. I know the minute delay is pretty normal;...