    TRANE MODEL: TUY060R9V3V3 SERIAL: Z313Y8F7G about 6years old.
    Thermstat calling for heat. Furnace does not purge or heating come on. Red LED is blinking about 1 time per second. Green LED blinks much more slowly. Yellow LED's at G, Y, & YLO, do not light up.
    5 amp fuse appears to be good.
    I put new batteries in the thermostat, no change.
    This is gas heat with an electric Air conditioner, not heat pump.
    Tempered R & BK, no change.
    Control is C341033P01 and labell inside furnace door panel say replace with CNT2536.? Don't understand why!
    I powered down outside breaker to AC, and inside power switch , no change except I could hear relay drop out upon each "power off /power down".
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jan 3, 2010, 12:06 PM
    Look on the back side of the blower motor access door for the blink/flash code legend
    Luke Moncrief's Avatar
    Luke Moncrief Posts: 3, Reputation: 1
    New Member
     
    #3

    Jan 3, 2010, 01:46 PM
    Looks like a normal heating call and that would be good. However, the furnace does nothing else.
    Please list next couple of troubleshooting items.
    I guess ignighter or other safeties
    Can you help more.
    Thanks very much.
    Luke Moncrief's Avatar
    Luke Moncrief Posts: 3, Reputation: 1
    New Member
     
    #4

    Jan 3, 2010, 01:47 PM
    Can you define further troubleshooting steps for me?
    Thanks very much!
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Jan 3, 2010, 02:02 PM
    That unit has a variabble speed draft inducer along with a 2 stage gas valve. This unit is not used friendly to service since many of the parts have to be replaced since the original trouble prone items are NO LONGER available. I suggest you have on site service for your unit.

    You can jump the thermostat out to eliminate it from the circuit for testing purposes .

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Trane xv90 troubleshoot [ 1 Answers ]

Can you tell me if I can reliably replace the existing but faulty CNT 03777 integrated furnace control with the next version (CNT 04985), or should I spend twice as much on the current version (CNT 05160)? Thanks

Do trane gas Furnace have belt and how to fix trane gas Furnace [ 1 Answers ]

I have trane gas Furnace and its stopped working the pilot is not working its keep shutting off and also the switch on and off is working but the pilot and burner is not working what should I do ?:(

Troubleshoot an oil furnace [ 1 Answers ]

I have an Oil Furnace and it will not start. I hit the reset next to it and it will kik on for about 30 sec but will I get not flame. It sprays the oil.

Trane furnace TDE080A945K2 not heating [ 2 Answers ]

We have a Trane furnace #TDE080A945K2 that hasn't been heating. It is just blowing cold air. We reset the furnace as instructed in the manual and after turning it back on it lights but then shuts off again after a minute or two and won't light again. We have cleaned the filter and the thermocuplar...


View more questions Search