    Does not heat
    I've got a York Heat pump that is not generating any heat. A/C mode works well, but starting late last winter (spring 2009), I started just using the emergency heat (its nat gas and I'm in TX so its realatively inexpensive). I'm wanting to try and diagnose the problem before I have a tech take a look at. Note that when I try to operate in heat pump mode, the indoor fan comes on as does the fan on the outdoor unit. I've left the unit on in heat mode for up to 1 hour and it did not heat up the house by one degree (have done this a couple of time in temps from 30 degrees to 45-50 degrees).
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #2

    Dec 29, 2009, 05:03 PM

    Does the vapor line (large, insulated) become warm/hot after the unit has run a while (5-10 minutes, check exposed section near O/D unit)? If not, but the system performs well in cooling, I would suspect a problem with the reversing valve or the outdoor metering device. System operating pressures in heating mode will reveal much of the mystery.
    dallasdude's Avatar
    dallasdude Posts: 2, Reputation: 1
    New Member
     
    #3

    Dec 30, 2009, 08:39 AM

    Thanks KC13. I'll check this out tonight.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Heat pump never turns on, handler blows continuous with no heat except with AUX heat [ 2 Answers ]

10 year old Rheem air handler RHBA-21J8MFCA, 1/3HP, 2.8A. New WeSt Columbia, SC 29170, Model 2HP13L48P-1B, HCFC-22, 4TON. Installed new out of box iN July and AC working splendidly but start-up is "violent" and loud. Installer says I need some sort of "start-up kit". I put off as had planned...

Unit conversion of specific heat to heat transfer coefficient (U factor) [ 1 Answers ]

I would like to know the conversion of "Specific Heat"(KJ/Kg/K) to "Overall Heat Transfer Coefficient"(W/m2/K) for the calculation of heat load. Looking forward for the answers. Immediate reply would be appreciated. Thanks, Rupesh

Carrier Hvac heat pump with aux/em heat- NO AUX HEAT [ 1 Answers ]

I have tried to install Honeywell 7500d thermostat. I get heat pump heat but no emergency heat although the termostate is calling for it. The installation manual says to see authorized agent if I have a dual 0/b on existing thermostat and another wire is attached to common. As of now, I have ...

Hunter 44155C Wiring - A/C turns on during heat cycle or heat will not shut off [ 0 Answers ]

Trying this again with the correct thermostat specs. Sorry, guys! It's a Hunter 44155C and the wires I have going into it are: White - W/B Red - Rh Green - G Yellow - Y1 Jumper from Rh-Rc


View more questions Search