    15 amp or 20 amp circuit breaker does it matter?
    Does it matter what size circuit breaker I use for lights or recptacles 15 or 20?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Dec 20, 2009, 08:59 PM

    14 AWG or 12 AWG wire can be protected by a 15 A breaker.

    14 AWG wire MUST be protected by a 15 A breaker.

    15 A outlets can be used on a 20 A circuit

    20 A outlets may only be used on a 20 A circuit

    12 AWG is more expensive than 14 AWG

    20 A outlets are more expensive than 15 A outlets.

    At 120 V; P (watts) = 120 * Current

    Suggest 3 conductor w/ground for switch loops. Allows timers and automation devices that require a neutral.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #3

    Dec 20, 2009, 09:01 PM

    15 amps using #14 wire should be enough, if you move up to 20 amps you need #12 wire and 20 amp breaker

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Adding a 200 amp breaker pannel to feed two 100 amp pannels [ 13 Answers ]

Hello all, This is my first post so I hope I do it right. This is what I got. The drop from the pole comes down to one 200 amp meter. The 200 amp meter feeds only one panel with a 100 amp input breaker and has many breakers that power the house (stove, water heater, dryer, outlets). Then it...

Can 20 amp line be run into a 100 amp breaker? [ 1 Answers ]

Hello, I am doing a remodel and have a open 20 amp breaker in my existing service. Can I run a temp line from the 20 amp breaker to my new box (which is not yet hot) into the 100 amp breaker. Just need to get some temp power up in the new space. Thank you

Identify 100 Amp vs 200 Amp Household Breaker Box [ 10 Answers ]

In my home Breaker Panel there are two breakers connected by a bar (labeled "Service Disconnect"), each breaker has a "100" written on them. Is this a 100 amp or 200amp Breaker box? Salesman wants to know what size Breaker Box I have in order to order to correct tankless water heater.

Running 2 100 amp breaker boxes on 200 amp meter base [ 1 Answers ]

I have 2 100 amp breaker boxes,but the meter base is 100 amp.Wanting to put 200 amp metet service with disconnect box.Can some one tell me if this is possible.and how you would connect the 2 breaker boxes to the disconnect box.Thank you


View more questions Search