    Circuit breaker ampere
    I have an existing dedicated circuit providing power to my residential well. It is a 240v circuit and has a 30 amps double breaker. I would like to install a manual transfer switch, "Emergen" (Conneticut Electric) model 10-7501 to the circuit, however they warn against connecting to any circuit having more than 20 amps. I assume this is rating limit of the transfer switch circuits. The pump motor of my well uses only about 10 amps to run... so my question is... can I replace the 30 amp breaker in the load pannel with a 20 amp breaker to comply with the requirements of the transfer switch, and still provide sufficient amperage to operate the well? I believe the wiring from the pannel to the well is 10 gauge if that is relevant.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #2

    Dec 5, 2009, 08:11 PM
    Well... you can try that. The starting load of the well pump will determine if it is acceptable. How do you know what the pump requires to run? 10 gauge wiring requires no more than a 30 amp breaker. Your pump may need less to run, but the distance between the breaker panel and the pump also is a factor in the wire size and the breaker capacity. If it was my installation, I would look for a transfer switch which could handle a 30 amp load... just my opinion.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Theory of vacuum Circuit Breaker & sf6 circuit breaker [ 15 Answers ]

I want to know about the basic Theory of vacuum Circuit Breaker & sf6 circuit breaker

Circuit Breaker trips because two bathrooms and master bedroom on same circuit [ 6 Answers ]

Some electrician committed a blunder in my opinion about 17 years ago. The master bedroom and two full bathrooms are all on the same circuit. If two hair dryers are used at the same time, it will trip the breaker every time. In figuring out what amperage would be required for two hair dryers and...

Circuit breaker trip after install of GFCI breaker [ 3 Answers ]

I'm replacing an outlet under kitchen sink that garbage disposer and dish washer were plugged into because they stopped working. The old outlet was not GFCI. So I'm attempting to replace it with one. Our home was built in the '50s and has no ground line yet. I used an extension cord to plug them...

Gfci breaker + outlet in same circuit.breaker tripping [ 4 Answers ]

I have a gfci breaker for a bathroom and there is an additional gfci outlet in the bathroom on the same circuit. The breaker was tripping intermittently over the past week and now will not re-engage. Should I suspect a faulty breaker or is it better to troubleshoot the circuit first? The...

Replacing a circuit breaker with a GFI breaker- q on neutrals [ 1 Answers ]

In process on installing withquestion on neutral wires. Do you take the neutrals out of the in the main panel neutral and put them in into the breaker where its labelled "load neutral terminal" and only have the neutral "pig tail" to the panel neutral bar? Thanks!


View more questions Search