Lennox Oil Burner Troubleshooting
HELP.
I have a Lennox OF23Q3 oil burner. It is tripping out the safety button on the primary control erratically during operation. Sometimes it runs 20 minutes before tripping and sometimes only a few minutes. When it does trip the blower just constantly runs until the power is cut.
I have changed filter, nozzle, cad cell, adjusted the electrodes. With no help. I have also jumped the cad cell terminals as described in the service manual. It did not trip off which is supposed to eliminate the primary control as a problem.
Any idea what I should be looking at to repair it? Perhaps the blower control board?
|
|
 |
Ultra Member
|
|
Nov 18, 2009, 03:58 PM
|
|
Could be a weak transformer, or a air leak in the line. Or even a bad pump, did you bleed some oil in a cup and look to see how much air there was, or any water?
|
|
 |
Ultra Member
|
|
Nov 18, 2009, 04:04 PM
|
|
Was the burner firing (flame present) at the time you observed the primary control lockout? Does the CAD cell have a clear line-of-sight toward the firing assembly? I doubt the blower control is contributing to the problem in any fashion.
|
|
 |
New Member
|
|
Nov 18, 2009, 04:13 PM
|
|
 Originally Posted by KC13
Was the burner firing (flame present) at the time you observed the primary control lockout? Does the CAD cell have a clear line-of-sight toward the firing assembly? I doubt the blower control is contributing to the problem in any fashion.
The burner was firing and I believe the new cad cell is aimed right at the flame/electrodes
I wonder why it would fire for 20 minutes before tripping the safety button? The safety button trips based on flame failure correct?
|
|
 |
New Member
|
|
Nov 18, 2009, 04:14 PM
|
|
The pump was bled and is air free...
|
|
 |
Ultra Member
|
|
Nov 18, 2009, 04:16 PM
|
|
The CAD cell is very similar to a photocell. Its resistance varies with the level of exposure to light. The primary control is seeking an acceptable resistance value to prove successful ignition & sustained firing.
|
|
 |
Ultra Member
|
|
Nov 18, 2009, 04:17 PM
|
|
Check for pinched/damaged CAD cell leads.
|
|
 |
New Member
|
|
Nov 18, 2009, 04:24 PM
|
|
OK I'll check the leads, perhaps replace them.
The old cad cell was dirty so not to take a chance we just replaced it.
Even though the furnace is 8 yrs old it is used in our 3 season 'camp' and has probably seen only a year's worth of use.
Thanks for your help.
|
|
 |
Ultra Member
|
|
Nov 18, 2009, 04:27 PM
|
|
With fuel oil units, more problems arise as a result of sitting idle than from running. Think of it as a diesel that is parked for months...
|
|
 |
New Member
|
|
Nov 18, 2009, 04:34 PM
|
|
Yes I have found that out ! I have an outside tank full of 50/50 fuel oil.
Usually use the LP gas logs for heat but the women use the camp and have trouble getting it lit.
|
|
 |
New Member
|
|
Mar 17, 2013, 11:55 AM
|
|
The furnace comes on and runs tills blower comes on , runs about 10 min. when blower stops, furance stops and furance will not come on again until you hit the reset bottom. This is when the house is cold.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Oil Furnace won't come on
[ 1 Answers ]
We have an old Williamson Oil Furnace. I'm not sure of the age, we bought the house 2 years ago. 3 days ago, it didn't come on, when the thermostat was turned up. The reset switch worked to get it started 2 mornings in a row, but now nothing. You can hear it trying to come on when the thermostat...
Upgrading oil
[ 2 Answers ]
Hi my name is justin. I have a 94 honda accord 2.2 liter v-tec I recently change my oil and upgraded 10w30 motor oil to 15w40 motor oil will 15w40 oil affect anything in the long run to the engine. ii get 135 miles on the car every day because I commute a long distance to work. I open it up meaning...
Burner does not stay on for a Lennox furnace
[ 3 Answers ]
I have a lennox 1994, 80% ignition, furnace. I am having a problem getting the burner to stay on until the house reaches the specified temperature. When the burner shuts down, the blower keeps running. In order to get the burner to kick on again, I have to fool with the thermostat such as turning...
60 year old lennox oil burner
[ 1 Answers ]
Yesterday I encountered a lennox oil burner. The pump will deliver oil only for 2-3 seconds then stop. I changed the dirty filter. Restarted the unit same thing happened. I can't see the make of the pump because of the one piece jacket . I believe it is an early model of the Sunstrand family. I...
View more questions
Search
|