    Weil Mclane ultra 155 settings
    I currently use my UG-155 as a back up heating system. My primary heat comes from my outdoor wood boiler. The OWB circulates water through the UG at 180°. I have set the HEATING limits on the UG to 140° as a back up in case the fire goes out. The DHW limit is set to 140°. However, when the DHW tank calls for heat, the boiler fires to 190° until the DHW requirement is reached. I want to set the boiler to not fire for hot water so I can stop using propane since Ive got the wood boiler.
    EPMiller's Avatar
    EPMiller Posts: 624, Reputation: 37
    Senior Member
     
    #2

    Nov 9, 2009, 08:23 PM

    You can mess those furnace controllers up if you get settings wrong, but all the info is in the installers manuals if you are confident of your understanding of the furnace. DON'T do it if you are unsure. Call a technician. I completely read the manuals before I did any adjusting of settings on the Ultra 240 (IIRC) that I am responsible for.

    EPM
    Chadco's Avatar
    Chadco Posts: 1, Reputation: 1
    New Member
     
    #3

    Nov 17, 2009, 10:21 PM
    Look in your manual, the older Ultras used a reference point of plus 50 degrees for the DHW setting, i.e. factory is 190 but shows up as 140 on the setpoint. The manual references do not change unless you are sure that the boilermate or other device is capable of that temperature. You should be able to find it in the control supplement that came with the installation manual, otherwise that manual is available online at Residential & Commercial Boilers, HVAC Equipment | Weil-McLain

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Just looking for some input on weil mclain ultra boilers [ 3 Answers ]

Hey guys. If any of you have worked on or installed ultra boilers, what kind of luck have you had with them, and if you have had problems, what were they. Have you found draft inducers to be problematic? Any other problems you have encountered? If so, please let me know what you have found. ...

Weil Mclain Ultra II 230 Boiler [ 25 Answers ]

I am considering a Ultra 230 boiler and in looking over the documentation I have three questions: 1. What the heck is a "condensing" boiler? 2. Will this boiler system work with cast iron radiators? 3. The piping diagram shows a 12" long connection atop the boiler between the input and...

Weil-mclain ultra 155 [ 3 Answers ]

I have power to my boiler because the fan is running, but no power to the electronics. So no firing, no sensing and no heat. Are there fuses in there that could be blown? Unit is 2 years old.

Weil-mclein ultra 155 [ 0 Answers ]

Just installed a weil-mclein ultra 155 bolier in my house with my neighbor who is a plumber. We got it up and running BUT, I'm am using 2 circulators for 2 zones with 2 thermostats, no domestic hot water. Manual fairly unclear about this setup. We can get it to run with 1 thermostat for 1 of the...

Weil-McLain Boiler settings? Look right? [ 3 Answers ]

Weil-McLain Gold Oil Model: WTGO-4 Series: 3 Net Output... Water 128 MBH Pressure set at 22 Water Temp at 162 Feet H20 at 40 Water Heater is Amtrol Boilermate WH7ZDW


View more questions Search