    Furnace burner cuts off when blower kicks in
    It's a Goodman GUPI100-4. Everything appears to work right until the furnace blower kicks in. Then the burner shuts off and the blower fan continues to run until I guess it cools down to its limit. After a minute or two it goes through the same cycle. HELP.:)
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #2

    Nov 7, 2009, 07:06 AM
    Does the LED on the circuit board start blinking when this occurs? If so, observe the # of blinks, then check service label for description. If not, try this: disconnect wires from "R" and "W" at thermostat and connect them together. If normal operation is restored, the problem is in the thermostat.
    fosterme's Avatar
    fosterme Posts: 3, Reputation: 1
    New Member
     
    #3

    Nov 7, 2009, 09:24 PM
    No LED on circuit board. Connected the two wires and it worked great. Will replace thermostat tomorrow and let you know. Thanks for the great help. For my info... what did the connection of the two wires do?
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #4

    Nov 7, 2009, 09:35 PM
    Apparently, the thermostat can't handle the gradually increasing load of the control circuit, and activating the blower relay is the proverbial "last straw", causing the control voltage past the thermostat to drop. Either the anticipator, selector switch, or "W" relay at the thermostat is bad. By connecting the wires together, you bypassed the thermostat so the unit could reach full operation. Good job.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Nov 8, 2009, 12:14 AM
    After disconnecting the old thermostat and before connecting the new thermostat I would jump the R or RH and W wires at the thermostat wire end that goes to the thermostat and check furnace for proper operation. This way you will also know if the thermostat cable going to the furnace is OK before hooking up your new thermostat. An extra 2 minutes work can save a headache after your new thermostat is hooked up.
    h2 uh oh's Avatar
    h2 uh oh Posts: 4, Reputation: 1
    New Member
     
    #6

    Nov 8, 2009, 03:44 PM

    Read this, may apply. Combustion/ Ventilation Air Supply Sizing Let me know if applies.
    fosterme's Avatar
    fosterme Posts: 3, Reputation: 1
    New Member
     
    #7

    Nov 9, 2009, 08:29 PM
    Replaced thermostat... works like a champ. Thanks KC-13.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #8

    Nov 10, 2009, 05:52 PM
    Glad to hear it. Playing "HVAC HERO" on PS-3 is really paying off... :D

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Furnace burner won't shut off but blower does. [ 1 Answers ]

Gas Furnace Issue: With this I keep the gas burner and the blower as separate components. My gas burner will usually shut off before the blower, but a couple of times in the last three days it has not. I will hear the blower shut off and the burner will remain on. As far as I know the burner would...

Carrier furnace blows 3 amp fuse after burner and blower fan have been on For a while [ 0 Answers ]

Carrier furnace with 4 LED control board 3 amp fuse opens after burner and circulation fan has been on for awhile 26Vac pulls down to 8 volts ac Replaced with 5 amp fuse and it does not open and furnace operation seams normal. Valve control is a White Rodgers 36E What should the resistance of...

Furnace Blower Won't Run Until Burner Quits [ 1 Answers ]

I have a 20+ year-old Carrier gas fired furnace that is logic controlled (that is, it has an electronic control unit in the top of the fan compartment). For some time, instead of starting the blower fan as it should after the burner has come up to a certain temp, the burner just runs until it...

Coleman Furnace blower kicks on and off [ 3 Answers ]

I have a Coleman model DGAT070BDE that is 9 years old. It has suddenly started acting strange. The blower motor will kick on and run for about a minute, then shut off for about 5 minutes and start all over again until I shut off the power to the furnace. The thermostat is not calling for heat as it...

Oil furnace, Burner cuts out [ 4 Answers ]

Ok, my original post was over a noisy draft regulator. Since then I have determined the cause of the regulator banging was the burner going out. This only occurs for a fraction of a second, just little pulses. I changed my in-line fuel filter and my burner nozzle. When I remove the inspection cover...


View more questions Search