    Spa and GFCI wiring
    I have a 240 amp line that is powering a hot tub installed before I bought the house. The line comes off the main panel in the house through a 50 amp breaker and is routed through a 30 amp GFCI and then to the tub. Pushing the test button on the GFCI does not trip the GFCI. Likewise, manually tripping the GFCI does not cut power to the spa. I opened the GFCI panel face and it is wired as noted below:


    Red (hot) from house connected directly to the red going to the tub with a wire nut

    Black (hot) from house connected directly to the black going to the tub with a wire nut

    White (neutral) from the house connected directly to the white going to the tub with a wire nut

    Ground wire from house connected to a ground bar

    Ground wire going to tub connected to same ground bar

    Wire connecting ground bar to GFCI

    My question is - is this wired incorrectly or is the GFCI simply defective?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Nov 19, 2006, 12:31 PM
    Quote Originally Posted by jbuda
    I have a 240 amp line that is powering a hot tub installed before I bought the house. The line comes off the main panel in the house through a 50 amp breaker and is routed through a 30 amp GFCI and then to the tub. Pushing the test button on the GFCI does not trip the GFCI. Likewise, manually tripping the GFCI does not cut power to the spa. I opened the GFCI panel face and it is wired as noted below:


    red (hot) from house connected directly to the red going to the tub with a wire nut

    black (hot) from house connected directly to the black going to the tub with a wire nut

    white (neutral) from the house connected directly to the white going to the tub with a wire nut

    Ground wire from house connected to a ground bar

    Ground wire going to tub connected to same ground bar

    wire connecting ground bar to GFCI

    My question is - is this wired incorrectly or is the GFCI simply defective?
    Since you say the wires are wirenutted from house to tub, how is the 30 Amp GFI connected? Sounds like the 50 amp breaker inside is the only breaker feeding the tub, WITH NO GFI PROTECTION FOR THE TUB!!

    If the 50 amp breaker fed the 30 Amp GFI and then to the tub, this would be fine, as long as the 30 amp GFI CB is large enough for the tub.

    I suspect someone discovered the 30 Amp CB is not large enough, and bypassed the 30 Amp GFI CB. So if this is the case, then a 50 Amp GFI CB is needed at the tub, in place of the 30 amp.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring Hot Tub and using a 50 Amp Double Pole GFCI Circiut Breaker [ 10 Answers ]

:confused: I keep getting the GFCI breaker tripping after wiring my hot tub. I wired 2 hot Red and Black to the proper terminals and the White to the neutral and the Bare Copper to the ground Post at the tub. I am using 6-3 w/G per instructions. Could the GFCI breaker be bad? When I wire...

Spa [ 1 Answers ]

Isn't UF for outdoors and THHN indoors? Also when you go to HomeDepot or Lowe's There big Hanging chart says "Outdoors use UF and with a 50 amp breaker use #8" ? Ok, Last question I hope. For my spa, Can I use THHN grade wire #6 copper(romex?)for outdoors if it is running through conduit ?...

Gfci spa panel tripping [ 4 Answers ]

I just installed a spa with 4 wires. The house is old and while the neutral & ground bus bars are separate in the spa panel, they are all on the same bar in the main panel. Do I need to install a ground rod by the spa panel to keep the gfci from tripping? (instead of running the ground back to the...

Spa wiring questions [ 4 Answers ]

I recently purchased a hot tub (spa). It calls for 6-3 with ground 240 volt 50 amp gfci breaker installed. I have almost completed the job and have some questions. I installed a 50 amp breaker in a subpanel in my laundry room and ran the 6-3 wire with ground down in the crawl space out to the...

Wiring a switch and GFCI circuit [ 3 Answers ]

I am in the process of wiring my bathroom. The lighting and fan circuit has one fan, one overhead light and one vanity light. I was wanting to use a NuTone single space / 3 switch unit for all three. Wiring that is all very straight forward but the fan requires a GFCI circuit to make it OK for over...


View more questions Search