    jab08's Avatar
    jab08 Posts: 8, Reputation: 1
    New Member
     
    #1

    Nov 1, 2009, 03:55 PM
    No heat
    My furnace inducer motor on my coleman furnace keeps cycling on and offf in 6-7 second intervuls but it never lights I have a code for a pressure switch but the stores are closed and I need a way to A. test the switch and B. bypass it to work till tomorrow it's 58 degrees in the house and dropping and I need help quick thanks for your time
    jab08's Avatar
    jab08 Posts: 8, Reputation: 1
    New Member
     
    #2

    Nov 1, 2009, 04:10 PM

    Also when I apply suction to the p/s switch the motr cycles but when it is disconectted at the switch the inducer motor will continuelly run it is clear at the orfice at the inducer motor
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #3

    Nov 1, 2009, 04:55 PM

    Blow threw the tubing on the pressure switch into the vent motor the is probably a blockage.
    jab08's Avatar
    jab08 Posts: 8, Reputation: 1
    New Member
     
    #4

    Nov 1, 2009, 08:33 PM

    I blew through the tubing on the pressure switch to the motor it was clear the furnace was still acting up out of sheer luck I started shaking the tubing all about while it was connected to everything and now the furnace is working I'm guessing it won't for long any ideas would be helpful thanks for the post josh if any of what I said helps me fix this or anybodies ran into this before your help is appreciated
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #5

    Nov 1, 2009, 08:51 PM
    Look closely at the pressure switch fitting where the hose connects. Do you see a small hole, about the same diameter as a paper clip? If so, try wrapping a piece of tape around the fitting to block the hole. If this works, either the switch diaphragm canister or the inducer housing may have a leak. This is just a quick fix until the real problem can be corrected. I would not recommend bypassing the switch, even on a short-term basis.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Nov 1, 2009, 08:56 PM
    If he does jump that pressure switch we might be reading about him in the obituary column in the paper. LOL.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #7

    Nov 1, 2009, 09:03 PM
    Yessir, then he will be a candidate for a geo system... ;)
    jab08's Avatar
    jab08 Posts: 8, Reputation: 1
    New Member
     
    #8

    Nov 3, 2009, 08:26 PM

    Lol hey gang a thousand thanks for the info I ended up tapping on the switch and it started working after the night I went and got a new pressure switch and they told me that coleman has had problems with the switch and lowered the resistance to trip it thanks again and yes we are all warm now
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #9

    Nov 3, 2009, 08:28 PM
    Glad you got it going.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Unit conversion of specific heat to heat transfer coefficient (U factor) [ 1 Answers ]

I would like to know the conversion of "Specific Heat"(KJ/Kg/K) to "Overall Heat Transfer Coefficient"(W/m2/K) for the calculation of heat load. Looking forward for the answers. Immediate reply would be appreciated. Thanks, Rupesh

Carrier Hvac heat pump with aux/em heat- NO AUX HEAT [ 1 Answers ]

I have tried to install Honeywell 7500d thermostat. I get heat pump heat but no emergency heat although the termostate is calling for it. The installation manual says to see authorized agent if I have a dual 0/b on existing thermostat and another wire is attached to common. As of now, I have ...

NO HEAT! Janitrol heat pump and AC system. Changing to Lux Thermostat. Wiring issue. [ 11 Answers ]

I have a Janitrol A/C and heat pump system. I replaced the thermostat with a Lux T9000LC The A/C works fine, but the heater does not. I have it wired as follows: G - Green Y - Yellow W - White RH - Pink B -

Hunter 44155C Wiring - A/C turns on during heat cycle or heat will not shut off [ 0 Answers ]

Trying this again with the correct thermostat specs. Sorry, guys! It's a Hunter 44155C and the wires I have going into it are: White - W/B Red - Rh Green - G Yellow - Y1 Jumper from Rh-Rc


View more questions Search