Hi,
I’m trying to reroute my bathroom DWV lines in advance of raising my house (to avoid a repeat of the seven feet of water we had several years ago). The existing layout, left on the attached diagram, has a vertical stack that continues underground to the street. I want to redirect the main to travel under the floor joints (right of the diagram) to the front of the house, where it would then travel vertically to the underground line. The cast iron main under the house and underground is 70+ years old and would be covered by a new concrete floor under the raised house.
To the point, would the proposed layout be acceptable? Venting is a concern but also the fittings I have in mind, which are: 1) 3” x 3” x 2” elbow with low heel, 2) 3” tee wye, and 3) 3” tee wye with cleanout.
Thanks for your insights.
|
|
 |
Senior Plumbing Expert
|
|
Oct 27, 2009, 04:56 PM
|
|
Hi Tom...
In my area the side inlet elbow wouldn't fly. In other areas of the country the side inlet elbow is OK. In my area, the tub must connect below the inlet to the toilet.
Check with your local plumbing inspector and see if a side inlet elbow is allowed when WET VENTING the toilet and tub using the lavatory vent. If not a 3"x2" wye may need to be substituted for the side inlet elbow.
If the end cleanout you proposed in your right diagram will not be accessible then opt. to eliminate the cleanout and dead end the run of 3" into the toilet.
Otherwise, as long as wet venting is allowed in your area, all looks very good!
MARK
.
|
|
 |
New Member
|
|
Oct 28, 2009, 12:28 PM
|
|
Mark,
Thanks very much for taking the time to review my diagram and comment on the situation.
Wet venting isn't a concern, but the fitting you mention could be. However, my illustration is misleading, reflecting my drafting skills. The elbow in question (#1) is 3 x 3 x 2 with a low heel, i.e. the 2" connection is at the rear of the bend, if that was not obvious (or matters). To make the tub connection, I would have to add an 1/8 turn elbow beyond the elbow.
Of course, if the toilet must connect above the tub inlet then my primary objective of raising the lines would largely be defeated. With the DW lines running under the joists, instead of vertically to the underground main, I was hoping to start the slope as close to the joists as possible to account for the slope toward the front of the house. With two sanitary tees and an elbow extending from the lavatory drain/vent to achieve the necessary arrangement, the main will hang well into the space below the joists (and I would undoubtedly hit my head - repeatedly).
I'll contemplate alternatives.
Thanks again,
Tom
|
|
 |
New Member
|
|
Oct 28, 2009, 02:03 PM
|
|
From the category of 'old dogs learning new tricks', I found the answer to my question about low heel elbows. They are intended for vent connections in vertical applications. My ignorance knows no bounds.
|
|
 |
Senior Plumbing Expert
|
|
Oct 28, 2009, 04:07 PM
|
|
Tom..
Check out the pic. Below...
If you add a 3"x2" wye on the horizontal as drawn below you should be all set.
Let me know...
MARK
.
|
|
 |
New Member
|
|
Oct 29, 2009, 08:46 AM
|
|
Mark,
Thanks for the reply. Your design is among those I had considered, but I was concerned about exceeding the maximum trap-vent distance for the tub. Before crawling under to take the appropriate measurements, perhaps you can clarify an important point. In your layout, would the trap-vent distance be considered the distance from the front of the trap to the wye or to the wye plus the distance to the vent stack? The difference is only a few inches, but the latter measure could exceed 6'.
Thanks again,
Tom
|
|
 |
Senior Plumbing Expert
|
|
Oct 29, 2009, 04:09 PM
|
|
Hi Tom:
As you can see in the diagram below, the 6'0" distance is the distance between the vent and the weir of the trap. You should be all set using the wye... :)
MARK
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Rerouting copper water lines in bathroom remodel project
[ 5 Answers ]
I am moving control valves for sinks, shower and toilet in a bathroom remodel project. The bathroom currently has copper plumbing. My questions are: 1. Is it possible/advisable to switch from copper to pvc to extend the supply lines for the new fixtures (2 sinks, 1 shower and 1 toilet are...
Rerouting Air Vent
[ 33 Answers ]
I am in the middle of a kitchen remodel, where I am removing a wall between a kitchen and dining room. After removing the wall, I found a 2" PVC air vent that is venting the the drain for the sink. The air vent extends straight up and out the roof. My goal is to re-route this vent into an...
Moving or rerouting a toilet vent
[ 13 Answers ]
I have a little privacy wall off to the side of the toilet in a 1/2 bath. We want to take the privacy wall out, and wouldn't you know it, that is where the toilet vent pipe is. Best I can tell (haven't stripped down the privacy wall yet), the pipe runs down into the foundation and connects up...
Drain rerouting
[ 4 Answers ]
My drain has a leak around the elbow joint, and I'd like to reroute from up my stair's kitchen drain. The line currently goes into wall and I like to run it through the floor and remove all the extract elbows and increase the flow before connecting to pipe in the basement.
Rerouting the kitchen vent pipe
[ 3 Answers ]
We want to put a window in our kitchen over the sink. After taking down the sheet rock, we noticed the 1 1/2" vent pipe is in the way. Would it still work correctly, if we put in some 90 degree bends to reroute the pipe, so it isn't in the way, & connect it back into the roof pipe, to prevent rain...