    Goodman furnace fault codes
    Hello !
    I am an auto mechanic, so when it comes to furnaces, I know nothing, but I have been learning about my furnce today.
    I have a goodman GMP-150-5 furnace that when the thermostat turns it on, I haer the draft fan start and run and after about 5 minutes, it just shuts down.
    Now, I looked at the ignitor which looked fine, but since it was not glowing and this is a common part, I replaced it with a new one (That was no help).
    I checked the fuse on the circuit board (good), and found out about the diagnostic codes. (The diagnostic code is flashing 3 blinks - would this cause these symptoms with the draft fan running and no ignitor glowing ?)
    I am going to remedy the problems shown by the diagnostic code, but I am unsure if there may be another problem since the ignitor is not glowing and I have 2 children coming home from school to a home with no heat, so I want to make sure I don't replace anoher part un-necessarily and still not be able to make it run.
    Thanks to anyone who answers this!
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Oct 28, 2009, 09:50 AM
    Look on the inside of the furnace blower for the code's or blink code. It will tell you the most likely place to start.
    Attached Images
  1. File Type: pdf Doc1.pdf (35.0 KB, 255 views)
  2. shoesvw's Avatar
    shoesvw Posts: 2, Reputation: 1
    New Member
     
    #3

    Oct 28, 2009, 01:59 PM
    Thanks for your help !
    There has been some progress - I cleaned out the bottom of the chimney (dirt nearly blocking the flue). The new problem is the ignitor now glows, (It didn't before) but no gas flame.
    I did a little poking around with a continuity meter and I found one of three heat sensors (don't know if this is the right term? ) has no continuity through it (This is a small metal unit with 2 wires on it, there are 3 of them mounted by the burner - one on top and one on each side-the wires run through all 3 of these, and it ends up at the gas valve).
    Since 1 of them was defective, I jumped across it and everything worked, but the burner got so hot it started melting the wires above it.
    Is this still a draft problem ?
    Thanks for any help!
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Oct 28, 2009, 02:24 PM
    You bet it is and right about now you should be calling for a On Site inspection from a professional before you destroy the furnace and possibly yourself.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

York Furnace Fault Codes [ 4 Answers ]

I have a York YP9C modulating furnace and matching York Affinity 8T 4 ton 2-stage condensing unit. The units are working wonderfully with no problems in the cooling mode. I have not used it for heating yet, so I do not know how it works in the heating mode. The furnace fault light shows a green...

Nedd fault codes for Coleman Evcon Furnace [ 4 Answers ]

I have a Evcon furnace model DGAA056BDTB and the cover plate for the controls box is missing. I am told that the fault codes were on the back of the plate. Where can I get a replacement cover or at least get the fault codes for my furnace?

Need goodman fault codes [ 3 Answers ]

Have an older goodman furnace. It goes all the way through start-up sequence (purge, igniter comes on, gas lights for a couple of seconds, then cuts off). It does this three times then shuts off. After this, the LED continuously blinks. I have no fault codes to troubleshoot the problem. Any Ideas?...


View more questions Search