    Double oven/cooktop wiring
    Hello everyone, I am in the process of adding a double wall oven to our kitchen,and I was just curious about a few things.OK the cooktop spec plate says 120/208 volts 4.7kw ,not sure but I don't think I worry about the 208 v markings.Correct me if I am wrong. I am in USA. Next it says 120/240 volts 6.3kw which if my math is good would be 26.25 amps. On its own 30 amp breaker. Supplied from the panel with 8 gauge red black white wires. The double oven plate says 120/208 volts 5.10 kw(again I don't think I need to worry about this reading). 120/240 volts 6.3 kw. That should be28.33 amps. Can I run 6 gauge red white black and ground( I think that's 6/3 with ground).Can I run that from the panel to a junction box near the 2 appliances,which they are next to each other, then branch off the 6/3 with 8/3 to each appliance. Another strange thing about the double oven the plate says 3 wire AC only, but it has red black white and green coming out of the conduit. And I will also change to 60 amp breaker if I am allowed to put both on the same circuit. Thank you for any help.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #2

    Oct 15, 2009, 07:50 PM
    ABSOLUTELY NOT!!
    Each appliance requires it's own circuit... with it's own dbl pole breaker. In the US, it's 120 / 240. And re-check your numbers... you have 6.3 KW listed with two different amperages. Ohm's law is an absolute.
    tryvector's Avatar
    tryvector Posts: 4, Reputation: 1
    New Member
     
    #3

    Oct 16, 2009, 04:21 AM

    Sorry , I miswrote the oven kw it is 6.8. Ok I will put them separate Does the 6/3 wire for the double oven seem like overkill.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #4

    Oct 16, 2009, 02:00 PM
    Yes. 10 ga. Wire for 30 amp circuits, 8 ga. For 45, 6 ga for 60.
    You can use a #8 with a 40 amp breaker for the dbl oven... and you may want to do that for the coktop as well... Doesn't the cooktop and the oven specify what amperage circuit to use?
    tryvector's Avatar
    tryvector Posts: 4, Reputation: 1
    New Member
     
    #5

    Oct 17, 2009, 07:42 AM

    Neither owners manual states amperage.The manuals are fairly useless.Thank you to everyone for all your help.
    tryvector's Avatar
    tryvector Posts: 4, Reputation: 1
    New Member
     
    #6

    Oct 17, 2009, 07:43 AM

    Neither owners manual states amperage.The manuals are fairly useless.Thank you for all your help.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Junction Box for connecting 220 Oven and Cooktop [ 1 Answers ]

I have a single 220 #8 3 wire cable that I want to install in a junction box the will let me attach those wires and then let me connect the wires running from the under counter oven and Cooktop to the junction box. I would prefer a box that has the screws that let me slide the wires in and then...

Separate cooktop/wall oven on same circuit? [ 2 Answers ]

I am remodeling my kitchen. It currently has 1 50A breaker for the electric range. I want to install a 36" cooktop and 30" wall oven. Can I install both of these on the existing 50A 240v breaker? I checked ratings for some of the models that I am considering, and combined they average about...

Installation of a gas cooktop over a gas oven [ 1 Answers ]

I want to install a gas cooktop over a built-in gas oven in a under the counter cabinet.. I understand that this configuration is not normally done.. (installation is normally a gas cooktop with an electric built-in oven combination)... Is there a code specification that I must follow for this...


View more questions Search