    Am going to run a new circuit about 115' underground to middle of front yard for xmas decorations and such. Will have 2 recepticals. What size wire and breaker will I need , and does it need to be in conduit?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Nov 12, 2006, 08:31 AM
    Since the xmas lights will probably be on for 3 hours or more, the circuit needs to be derated by 80%, so a 20 amp circuit should have no more than 16 amps or 1920 watts of load.

    One two wire circuit, 120 volts drawing 16 amps at 115 feet will need #8 copper wire, to keep the voltage drop below the recommended 3% for a branch circuit results in 2.8%Vd at the end of the circuit.

    If you run 1- 20 amp circuit, using a 20 amp GFI breaker, to protect the entire circuit, (a GFI outlet will not be sufficient for this situation), you can:

    1.Use #8 UF 2 wire with ground cable, can be 12 " deep.

    2. Use a 3/4" PVC conduit, with 2-#8 THHN/THWN and 1-#10 THHN/THWN green for the ground (or XHHW for both), 12 inches.

    3. Use metal rigid conduit with the wire from option #2, you can go 6 inches deep.

    If you need more than one 20 amp circuit, options #1 & 2 do not apply. UF cable then goes to 24" deep, and PVC conduit goes to 18" deep.

    Any buried cable or conduit should have a warning tape several inches above it.

    Thous metal conduit is the most expensive raceway to purchase and install, sure allows someone to save back pain by digging a shallow trench.

    And may be best to check with any local codes due to local soil conditions.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Circuit watts [ 1 Answers ]

Can any one please tell me the difference between watts per luminaire and cuircut watts per luminaire

Am I overloading a circuit? [ 2 Answers ]

I just bought a house and moved in last week. It was hot and humid up here in the northeast so I had an window A/C unit (5,000 BTU) cranking in one of the bedrooms. Every time the unit's compressor kicked in, lights in other parts of the house dimmed. This is my first home and I'm just starting to...

Gfi circuit [ 1 Answers ]

I was wondering if when wiring for 2 gfis for different circuits, do I need separate neutrals for each or just a common one

Outside GFI circuit - 15amp outlet on 20amp circuit [ 1 Answers ]

I need a better understanding of what I should do when setting up my new outdoor circuit. I've got a circuit that runs about 150 feet, so I'm installing 10g wire to allow for the voltage drop. I read in the Home Depot Electrical 123 book that I can have at most a 15amp circuit with 10g wire on...

Circuit breakers [ 2 Answers ]

I would like to up grade the amps going to my garage so I can run my saws and power tools with out dimming my shop lights. I currently have a old style fuse box in the garge feed with 12ga uf cable run off a 20amp circuit breaker in the service panel. My plans are to replace the fuse box with a new...


View more questions Search