    I am in the process of re-wiring my house. My load center used to be located on the outside of my house. I have now moved the load center (200 amp sq d qo panal) to the inside, and am looking to place a 200 amp disconnect next to the meter pan. I was told I needed to get 2 awg 3 cond with ground to run from the dieconnect to the load center. I recently went to the local supply house to buy 2 awg 3 cond with ground romex, because I was told the wire needed to be in a jacket. I was told at the supply house that they do not make 2 awg 3 cond with ground romex, and I would have to run it in Allum. I would rather not run Allum. I would like to run copper if possible. Can anyone tell what my options are.

    Thanks in advance
    Jim
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Nov 11, 2006, 06:15 AM
    It is a good thing that you did not listen to the person that told you to use #2/3 cable for a 200 Amp service, as #2 copper is rated to handle anywhere between 95-130 amps,depending certain specifics.

    There may have been a misunderstanding, as #2/0 copper is allowed for a residential 200 amp service. Or you can use #4/0 aluminum.

    If a cable assembly is made using #2/0Cu , it is not widely available, so if you want to use copper you may need to run conduit. Besides, copper is very expensive now. Also, if any cable will be outdoors the sheathing needs to be sunlight resistant, and Romex is not.

    So, for 3-#2/0 THHN or XHHW cables and 1-#6 cu for the equipment ground, you need 2" conduit, Sch40 PVC is probably the most available and the easiest to work with.

    If the disconnect can go close to the meter, you can use 2" conduit nipples, locknuts and bushings between both and use #2/0 Cu between the meter load side and the disconnect line side.

    What is widely used and available for residential 200 amp service is #4/0 SER 4 wire aluminum cable. Aluminum is very popular for large amperage feeders.

    The issue with Al wire is to be sure to treat the connections properly, by wire brushing, applying anti-oxidant compound, and proper torqueing the connection. Any disconnect, panel, and meter will list the torqueing specs for their connectors, which must be followed with both Cu and Al cable.

    See the following spec sheets found at www.alcan.com:

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

200 Amp [ 1 Answers ]

I Am Having A Home Built That Is 3800 Square Feet. The Home Will Have 2 Furnaces, 2 Air Conditioners, 2 Refrigirators, And A Deep Freeze. All Other Appliances Will Be Gas. I Have Voiced Concerns About The Availability Of Unused Circuits On The 200 Amp Panel To Be Able To Finish The Basement In...

200 amp or 100 amp [ 6 Answers ]

Which is better, a 100 amp circuit box or a 200 amp circuit box?

200 amp service with a 200 amp outdoor breaker [ 1 Answers ]

I need to know how to wire a 200 amp outdoor breaker enclosure.I have 4/0 scu cable for my service head to the meter,and 4/0 scu from meter to breaker enclosure.Then from the breaker enclosure I have 4/0 ser cable to my panel.What is the proper wiring method in the enclosure,please help.

200 amp [ 2 Answers ]

Looking for opinons for panel boxes ge square d cutler hammer murray Also what does 30/40 spaces mean. Thanks for any info.

200 Amp Outside Service Disconnect [ 5 Answers ]

I NEED TO KNOW IF A "200 AMP OUTSIDE SERVICE DISCONNECT" IS THE SAME THING AS A "200 AMP OUTSIDE MAIN BREAKER OR LOAD CENTER"? SOMEONE PLEASE HELP ME!! HOME DEPOT WAS USELESS.:confused:


View more questions Search