    Hi I am having trouble with my panel, I have installed two 240v/2000w base board heaters and a thermostat. In my panel I have a 2pole 20amp breaker, the black and red wires are connected to the breaker and the ground to the ground bar, the wire runs to the thermostat which is a 240v double pole, they attach to the thermostat to the line in red on red and black on black, grounds to the box. From there they go out to the first heater and again red on red and black on black. From the first heater to the second and connected to the same wires coming from the thermostat. I cannot get any power, I checked the power at the breaker and get no reading on the meter. I tried a 40amp double pole breaker in place of the 20 amp and the same thing no reading. I checked all the other breakers in the panel and they all have power going out. Can you help as I am stumped.

    Thank you
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Sep 6, 2009, 02:48 PM
    What brand of panel is it?
    Are you in the US? I assume you are in Canada since you are using black, red and ground cable.
    mjherman's Avatar
    mjherman Posts: 4, Reputation: 1
    New Member
     
    #3

    Sep 6, 2009, 03:00 PM

    Yes I am in Canada and the box is a federal and uses stablok breakers
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Sep 6, 2009, 03:21 PM
    You probably have the breaker installed wrong. It is possible to install an FPE two-pole breaker so that it is contacting the same buss. A two-pole MUST contact both busses/stabs.
    mjherman's Avatar
    mjherman Posts: 4, Reputation: 1
    New Member
     
    #5

    Sep 6, 2009, 03:38 PM

    I went out and tried that and it is working thank you very much, I am a happy man!!
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #6

    Sep 6, 2009, 03:50 PM
    I love an easy fix. :cool:
    mjherman's Avatar
    mjherman Posts: 4, Reputation: 1
    New Member
     
    #7

    Sep 6, 2009, 04:29 PM
    Yes me too, while I have your attention, Does a welder require the same outlet as a drier or a stove?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #8

    Sep 6, 2009, 06:00 PM
    Typically no.

    A dryer is a 120/240v-30a line.
    A range is a 120/240v-50a line.

    A typical stick welder requires a straight 240v-50a line. Although it could be wired to work on a range receptacle if you change the plug and just wire the two hots and the ground.
    Tev's Avatar
    Tev Posts: 232, Reputation: 20
    Full Member
     
    #9

    Sep 7, 2009, 05:36 PM

    One small problem that may or may not apply to Canada.

    Fixed electric space heating equipment is considered a continuous load. 4000W at 240V is 16.67 amps. The max continuous load allowed on a 20 amp circuit is 16 amps. Although it should be fine with the small amount that it is over it should have been installed with 10AWG wire and either a 25 or 30 amp breaker.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Baseboard heaters? [ 1 Answers ]

Help , I do not understand the diagrams to a plf series Fahrenheat eletric/hydronic heater . There are a blck, and a red and a black and a red and a green . The same for the 2 pole therrmostat. One says L1 The power source is black ,red,white and ground . Help Sharon:confused:

New to baseboard heaters [ 24 Answers ]

Hello; I need a lot of electrical help/advice. I am trying to install an electrical baseboard heater in a basement room (15'X10'). My friend helped me already do the following: Run the conduit and electrical box for thermostat Pull all the wires Mounted the baseboard heater to the wall We...

Baseboard heaters [ 2 Answers ]

I have some used baseboard heaters I want to install in my basement. 1) They have two wires on the unit itself and four wires on the thermostat, can I assume my power coming in must go to the thermostat first and then to the heater? 2) The four wires on thermostat are labeled L1 & L2 and T1...

Electric baseboard heaters -wiring 1 thermostat to two heaters [ 2 Answers ]

I would like to heat my new garage with electric baseboard heaters. The new garage is 20X24 feet. I would like to use only one 240V #12 2 wire circuit running two heaters at a total of 3800 watts. I plan to use 2 pole 20A breakers and 2c #12 wire. I would like to have both heaters controlled...

Baseboard heaters [ 12 Answers ]

Hi all.. New to the forum.. Thanks in advance for any help.. I am trying to set up new baseboard heating in my basement.. My questions are to what size breakers to use and if I can put it all on one circuit.. I want to set up 3 rooms: Room 1 - 2 1000 watt heaters Room 2 & 3 - 1 1500 watt...


View more questions Search