New Member
|
|
Aug 31, 2009, 08:36 AM
|
|
Install honeywell rth230b with six wires
Hi,
I am replacing old honeywell thermostat with rth230b model.
There are 6 wires comes from the wall. I have connecterd GYW and R to Rc.
Heat works fine. Then AC starts fan works but outside unit do not start up.
Looking at the wire diaramm looks like one I need power to Cool relay which means
Either blue or orange should go to Rc and existind R should be moved to Rh.
What should I do? Thanks
|
|
 |
Uber Member
|
|
Aug 31, 2009, 08:46 AM
|
|
Rh and Rc should be jumpered together.
|
|
 |
New Member
|
|
Aug 31, 2009, 08:48 AM
|
|
Sorry to mention this: Rh and RC are jumpered together. Also. This is gas heater with AC unit outside. Thanks
|
|
 |
Uber Member
|
|
Aug 31, 2009, 09:32 AM
|
|
Y controls the outside unit. It's possible that the breaker popped when doing the upgrade. If your comfy, you can remove the panels from the outside unit after turning it off and watch the contactor.
If you connect Y to R, temporarily, the outside unit should start. There are delays built into the thermostat and sometimes the outside unit. They can range from 1-5 minutes before it can turn on after an off.
|
|
 |
New Member
|
|
Aug 31, 2009, 09:39 AM
|
|
KISS, If I understood correctly I should not even try connecting blue or orange wire to RC? There is 5-wire connection diagram in the thermostat instruction. Do you think it does not aplpy to my case? Thanks
|
|
 |
Uber Member
|
|
Aug 31, 2009, 09:49 AM
|
|
Bet the other wire is C. C is optional. Not necessary if stat is battery powered.
Check the AC breaker. Not the one for the heater.
|
|
 |
New Member
|
|
Aug 31, 2009, 09:52 AM
|
|
I did. I actually turn Heater and AC units breakers off on the electrical panel before I did install on back on after...
Thanks
|
|
 |
Uber Member
|
|
Aug 31, 2009, 10:00 AM
|
|
Y to Rc, should turn on the outside unit. One reason why it would not, is if for some reason you had two transformers.
What terminals were used on the old stat?
|
|
 |
New Member
|
|
Aug 31, 2009, 10:03 AM
|
|
Old stat has matching GYWR and I did not label B and O :((((
|
|
 |
Uber Member
|
|
Aug 31, 2009, 10:09 AM
|
|
If you had wires connected to B/O then you have a heat pump and your cuurnt stat won't work. It's made for gas/oil and possibly electric furnaces.
The outside unit runs in both heat and cool modes if you have a hP.
|
|
 |
New Member
|
|
Aug 31, 2009, 10:11 AM
|
|
There is no HP it is just AC unit. Outside unit does not run at all now. Thanks
|
|
 |
Uber Member
|
|
Aug 31, 2009, 10:16 AM
|
|
Besides the tests I told you to do, I'm out of options.
a) There is a rare case where there are two transformers - Rc and Rh went to different wires.
If you temporarily connectt R to Y, this rues out the stat.
If your able to observe the contactor in the AC unit, this rules out the wiring.
|
|
 |
New Member
|
|
Aug 31, 2009, 10:22 AM
|
|
Thanks - I'll try those tests. There is also second stat upstaires which I did not screw up yet - I am going to look at the wiring there.
Thanks again.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Too many Wires and Honeywell RTH230B
[ 5 Answers ]
In the middle of our remodel, our thermostat stopped working last night, 1 hour before the hardware store closed. (It wasn't the batteries or the breaker.) I got a Honeywell RTH230B. Out of frustration from the remodel taking so long and the new problem, uncharacteristically I just took the old...
Honeywell rth230b
[ 1 Answers ]
I am trying to install the honeywell programmable t-stat rth230b. The problem is my old two-wire thermostat has red and green wires . Where do the hook-up on the new one? Thanks
How do I install a new Honeywell RTH230B from Honeywell T8195B
[ 1 Answers ]
Good evening.
Our old thermostat was model T8195B which came with wires C,Y,W,R & G. has no rererence as to where they hook up. The new one RTH230B doesn't say where these wires go. I've removed the Rc/Rh jumper according the instruction manual. Nothing went on at all. What can I go
Thank...
Install Honeywell RTH230B, Removing Honeywell Q674L
[ 2 Answers ]
I am removing a old (1987) Honeywell Mercury THermostat Q472L Base that has W, R, Y, G, B, O. The RTH230B has Rc (which I assume to be B), Rh (which I assume to be R), Y (to Y), W(to W), G (to G). I have no idea what to do with the O (which I read could be the Changeover.
Do I just tape it up...
View more questions
Search
|