    30 amp generator installed to a 60 amp transfer switch?
    THis is the generator I want to install, 6800 Watt Portable Genearator ELECTRIC START

    # Wattage

    * Running Watts: 6800 Watts
    * Maximum Watts: 8500 Watts


    my plan is to mount a box on the outside of the house, with the 120-240V L14-30R inlet, so I can plug a extension cord if I need it or move the generator when I don't need it. Now my question is, do I use #6 copper for x y w and ground in a rubber jacket wire ? If that is so I am assuming x is pulling 30 amps and y is pulling 30 amps, which means that I need the 60 amp panel! Is my thinking right ? Thanks guys for you input in advanced!
    onamission1's Avatar
    onamission1 Posts: 21, Reputation: 0
    New Member
     
    #2

    Aug 21, 2009, 10:47 PM

    Oh I am not asking about any wiring info about from the main panel to the transfer switch panel but I am planning about running teck outside to the plug or use a 6x6 box and come out with a LB down with pvc into the plug. Is this what you would do ?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #3

    Aug 21, 2009, 11:51 PM

    Draw a 240 V load and two 30 Amp breakers in series.

    Now is it 30 or 60?

    Why not use an interlock kit and ditch the transfer switch.
    onamission1's Avatar
    onamission1 Posts: 21, Reputation: 0
    New Member
     
    #4

    Aug 22, 2009, 12:56 AM

    I don't know is this generator able to kick off 60 amps? That's my question ! I am using a interlock kit I'm just refuring to it as a transfer switch
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #5

    Aug 22, 2009, 04:31 AM

    You have a L14-30R Receptacle, that is for 30 Amps.
    You could run 4 #10's from Inlet Box to Panels Top Right Breaker(need a 30 Amp 2 pole for Generator), Add an Interlockkit, and your done. You may have a couple of 120 Volt recepticles on your Generator you could use as well.
    onamission1's Avatar
    onamission1 Posts: 21, Reputation: 0
    New Member
     
    #6

    Aug 22, 2009, 08:28 AM

    Hmmm okay so its only 30 amps eh... thanks but can I use a 60 amp breaker with a 30 amp generator? Would that hurt an
    onamission1's Avatar
    onamission1 Posts: 21, Reputation: 0
    New Member
     
    #7

    Aug 22, 2009, 08:29 AM
    Anything ?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #8

    Aug 22, 2009, 08:31 AM
    NO. You use a two-pole 30A breaker as your backfeed breaker.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Generator transfer switch [ 1 Answers ]

How difficult is it to install a generator transfer switch? It's pre-wired, doesn't look too Difficult. Is there anything I should look out for? The only thing I'm not sure of is it comes with two 15-amp 1-pole breakers, two 20-amp 1-pole breakers, and one 2-pole 20 amp breaker. How do I tell the...

Generator transfer switch - enough for well pump [ 1 Answers ]

I have a 10hp 5600 generator that I want to connect to a "GenTran 20216 Manual Transfer Switch". It states that this transfer switch has 6 switches (rated 15 amps ea), a handle tie for one 2-pole circuit such as a well pump. My question is this - my well pump is 220 30 amps. Does two switches at...

Generator power transfer switch [ 1 Answers ]

Our power goes off on a frequent basis. If it is off more than 8 hr I need to power up with my own generator 8kw, to prevent spoilage and to run the well. My question is do you have to disconnect the neutral also and run the neutral to the generator or can the neutral be common to both power...

3 wire 220 connecting transfer switch to generator [ 2 Answers ]

I have a manual transfer switch that I want to use between my house circuits and my 5000 watt generator. I have 3 wire #10 receptical existing from the circuit box over to where my generator sets (it is exhausted outside). Can I use this 3 wire line to connect my transfer switch to my generator...

Transfer Switch & Generator Compatibilty [ 3 Answers ]

I have installed a manual transfer switch in my home. It says in the instructions to make sure the neutral is un-bonded to the generator. My Generator has a bonded neutral to the frame. What can I do to make the switch and the Generator compatible? Thanks


View more questions Search