    If I install 120v receptacles on the outside of a building, an open porch (wet location), does the recptacle have to be WR type rated?
    kww67's Avatar
    kww67 Posts: 2, Reputation: 1
    New Member
     
    #2

    Aug 10, 2009, 07:42 PM
    The answer is yes. Any 15A or 20A, 125v receptacle installed in a wet location must be of the WR type. I am a state electrical inspector and was just learning to use this feature.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #3

    Aug 10, 2009, 07:56 PM


    The answer is no.

    An open porch would not be considered a wet location. An open porch would be considered a damp location.

    “shall have an enclosure that is weather proof when the receptacle is covered (attachment plug cap not inserted and receptacle covers closed).
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Aug 11, 2009, 02:38 AM
    HK, read Section 406.8 (A) of the 2008 NEC, any receptacle in wet OR damp location shall be rated weather resistant.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #5

    Aug 11, 2009, 03:52 AM
    TK's point is important.

    Not everyone is under the 2008 NEC, and some have exceptions not requiring TR's.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #6

    Aug 11, 2009, 05:29 AM

    No, Stan I was just wrong. But I do blame it on old code book. But at least I checked before I put my foot in mouth.
    Going to get new code book at first chance. I don't need help from old code book to be wrong. I can do it all by myself.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

15 amp receptacles [ 2 Answers ]

How do you figure how many 15 amp recp. Can go on 20 amp circuit

20 amp receptacles [ 1 Answers ]

How do you figure how many 20 amp recp. Can go on 20 amp circuit

Electrical receptacles [ 1 Answers ]

I am running # 12 wire into a 15 amp receptacle and would like to run that to a outside 20 amp receptacle can this be done

Type I and Type II Errors (Statistics and Probability) [ 1 Answers ]

A researcher studying stress is interested in the blood pressure measurements of chief executive officers (CEOs) of major corporations. He believes that the mean systolic blood pressure, of CEOs of major corporations is less than mm Hg, which is the value reported in a possibly outdated journal...

15 or 20 amp receptacles? [ 6 Answers ]

I had my electric service upgraded 18 years ago and had the electrician install two GFCI's, One for the bathroom and one for the kitchen. They are on separate circuits by themselves. They are each on a 20 amp breaker with 12 gauge wire and the GFCI's are rated 15 amp with 20 amp feed through. My...


View more questions Search