    Max continious wattage on a 15A breaker and 20A breaker
    What is the max continious wattage on a 15amp and 20amp breaker?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Aug 7, 2009, 07:52 PM

    Can't solve the problem with the information given. Power = Voltage * Current; What's missing?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #3

    Aug 7, 2009, 07:55 PM

    OK. I'll be nice. 80% of the breaker rating gives you the max current. You know the rest.

    Any load on for more than 3 hours at a time is called a continuous load and the circuit needs to be derated or multiplied by 1.25 which is 1/0.8
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Aug 8, 2009, 03:12 AM
    This may be a first,

    Quote Originally Posted by KeepItSimpleStupid View Post
    OK. I'll be nice.
    Finally making progress!

    Only kidding Kiss.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #5

    Aug 8, 2009, 05:41 AM
    Quote Originally Posted by KeepItSimpleStupid View Post
    OK. I'll be nice. 80% of the breaker rating gives you the max current. You know the rest.
    Actually 100% of the breaker rating gives you the max current. There is no blanket "80% rule" for breakers. This only applies to certain loads.

    Quote Originally Posted by KeepItSimpleStupid View Post
    Any load on for more than 3 hours at a time is called a continuous load and the circuit needs to be derated or multiplied by 1.25 which is 1/0.8
    Actually any load expected to be on for 3 hours or more is considered a continuous load. Very little in a home would be considered a continuous, although there are things such as electric heat and water heaters that are specifically by code considered continuous loads.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

I just replace my breaker box but it didn't have a main breaker is that safe ? [ 5 Answers ]

On the box it says it is a 100 amp breaker box and I have 1 50 amp breaker .2 30 amps breaker and 3 20 amps breakers if I add all the breaker it is 170 amps and my breaker box is for 100 amps is that how it works? Do I need a bigger breaker box? Is it unsafe...

Gfci breaker + outlet in same circuit.breaker tripping [ 4 Answers ]

I have a gfci breaker for a bathroom and there is an additional gfci outlet in the bathroom on the same circuit. The breaker was tripping intermittently over the past week and now will not re-engage. Should I suspect a faulty breaker or is it better to troubleshoot the circuit first? The...

How do I determine breaker amps on a 240v double breaker? [ 7 Answers ]

Hi, I have a new elec. Cooktop that needs 240V, 40 amps. Each pole of the double pole breaker for my cooktop circuit Says 30amps. So can this 240v circuit support 60 amps, or just 30? Thanks!

Bathroom GFI outlet trips breaker at breaker panel [ 2 Answers ]

Hello all. Our house is approximately 13 years old. Each morning when both the iron and blow dryer is plugged into two separate GFI outlets in the master bathroom, the circuit will trip the 15 amp breaker in the breaker panel. Is it possible to upgrade the breaker to a 20 amp without...

Replacing Circuit Breaker with Higher AMP Breaker [ 8 Answers ]

Excuse me, I did look at the code book as is suggested in your Sticky. The NFPA may answer this question, but I am not knowledgeable enough to recognize it: Our offices are upstairs in an older (renovated home) building with modern wiring. We have 4 computers, 3 printers, and miscellaneous with...


View more questions Search