New Member
|
|
Oct 18, 2006, 03:33 PM
|
|
Multifuel stove not heating radiators
Hi there, we have recently had a multifuel stove fitted, it has a 40,000 BTU boiler fitted and is not heating the radiators, the manufacturer says it will run 16 rads, but we only have 13, 7 rads but 6 are double, we have a roaring fire and turn the pump on the and they are lukewarm and don't get any hotter. Our central heating engineer who fitted the system says there is no air blockage.
|
|
 |
Ultra Member
|
|
Oct 18, 2006, 03:43 PM
|
|
It almost has to be a vapor lock or bad pump. What is the temperature at the supply and return. Are there any purge and balance valves, or other type of valve that is not fully opened?
|
|
 |
New Member
|
|
Oct 19, 2006, 09:23 AM
|
|
 Originally Posted by NorthernHeat
It almost has to be a vapor lock or bad pump. What is the temperature at the supply and return. Are there any purge and ballance valves, or other type of valve that is not fully opened?
It gets hot in 2 of the pipes but when you put the pump on they immediately go cold and stay cold, not sure about the valves thanks
|
|
 |
Uber Member
|
|
Oct 19, 2006, 10:08 AM
|
|
Something sounds strange. How experienced is your engineer? There may be a mistake Northern Heat never imagined anybody would make. If the pipes immediately go from hot to cold, they have cold water flowing in them. There may be another answer, but I wonder if the make up water line is connected to the pump intake? Check your water meter to see if it moves when the pumps run.
Study the pump. There should be a line running from the boiler to the center of the pump. Then another line should come off the outside edge, perhaps a snail shell looking thing, and connecting to the lines to the boilers. Any valves should be wide open. Modern ball valves will have the handle parallel to the line when open. With an old gate or globe valve, you just have to try turning the handle back and forth. Post back with what you find.
|
|
 |
Ultra Member
|
|
Oct 19, 2006, 02:49 PM
|
|
Something is goofy in Denmark. I don't think its taking on too much make-up water. The reason is a boiler will run about 12 psi. cold and 18 psi hot. It's a sealed system and if it starts to take on make up water the pressure should go above 30 psi when the pop-of/relief valve will let the pressure go. Unless you have a leak in the system it's not taking on fresh water. Also, of coarse when you turn on the pump cold water from the radiators flood the boiler and it turns cold. There are 2 pipes in and out of the boiler that go to the radiators. The pump should be on the return side. Let the boiler run with the pump-on (never when it is off) after 1 hour record the water temp' at the pump pipe and the other one of the same size (the supply) lets se what you've got.
|
|
 |
New Member
|
|
Oct 22, 2006, 03:18 PM
|
|
Thanks for your help, but we have had another engineer in and he thinks it's the chimney that needs lining as he says that the fire is not drawing enough, I'm still very confused but will give it a try and see if it helps.
|
|
 |
Uber Member
|
|
Oct 23, 2006, 05:52 AM
|
|
Does your roaring fire have a blue flame? If so, I doubt the problem is the draft. Give Northern Heat the info he asked for and try to work with him.
|
|
 |
New Member
|
|
Jan 7, 2012, 09:53 AM
|
|
ive have same problem, 25kw stove and it won't even heat 8 rads upstairs with the downstairs rads switched off. Had plumber out today and i was losing heat going to the oil burner outside!! Have closed the valve and seems to work. But need a good roaring fire to get it going!!
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Radiators not working properly
[ 7 Answers ]
I hope someone can please help. We have had problems with our heating system (2 years old) for the past 2 months and have had the people who installed it working to repair it.
First the boiler stopped working properly. After a new pump, heat exchanger and circuit board were fitted, the boiler...
Old radiators + new boiler are boiling us alive
[ 6 Answers ]
Help! We recently installed a new boiler and pump in our 77-year-old home. The water pressure is great, but too much for our old boilers. They are incredibly hot and can't be turned off. Our plumber has been searching for new valves to fit to the old radiators, but without luck. Any ideas?
Warm radiators when the heating is off, and hot water is on
[ 0 Answers ]
Please Help,
Does anyone know what the problem is with my central heating system. The radiators in the house are warm, but I have not been calling for central heating, only water. Radiators are warm both upstairs and down.
I have a gas fired boiler down stairs in the kitchen and hot water...
Moving steam radiators
[ 2 Answers ]
I would like to relocate single pipe steam radiators, basically swap some around by putting larger ones (in colder areas) where small ones are and vice versa. It seems that it should be easy enough to close the valve, disconnect the radiator and relocate. I have no education on this though and I am...
Moving radiators
[ 1 Answers ]
I would like to relocate single pipe steam radiators, basically swap some around by putting larger ones (in colder areas) where small ones are and vice versa. It seems that it should be easy enough to close the valve, disconnect the radiator and relocate. I have no education on this though and I...
View more questions
Search
|