    Copper/Aluminum SEC
    110.14 prohibits the use of conductors of dissimilar metals in the same terminal or connector unless the terminal/connector is identified as for that purpose. As a result, need some advice from the pros.

    The SEC on both sides of the meter are the original aluminum. I updated and relocated the main breaker panel board, but installed a service disconnect in the original panel location to stay within five feet of the meter, per local code. I used copper for the feeders (code allowed) and in the interim the service disconnect SEC is the aluminum (either allowed for SEC). I eventually want to use copper from the disconnect to the meter, but then I would have a copper/aluminum combo under the neutral terminal, a violation of 110.14. I know aluminum is used a lot for SEC, I guess I just have a phobia about aluminum. The house was originally wired with aluminum, and I found some real scary stuff when I was rewiring the house. Honestly, I'm surprised the house didn't burn down ages ago.

    1. From a practical (and cheaper:eek:) standpoint, should I just stick with the aluminum on the line side of the disconnect?
    2. If I had the SEC from the service drop replaced with copper, are special connectors used for copper to aluminum? The service drop is aluminum.
    3. I would call my utility for details, but generally, are electricians allowed to replace/connect the SEC to the service drop?
    4. Finally, how long has 110.14 been in effect? I'm asking as my system is grounded at the meter, but the electrician connected the copper ground wire under the neutral terminal in the meter case, which uses aluminum SEC. The house was built in 1966.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Jun 29, 2009, 06:14 PM
    Well, there should be no place where the line and load neutrals share a terminal. Each should have it's own.

    Yes, there are special connections when CU must be connected to AL. Service drop splices have a plate that separates the two conductors.

    Some electricians are, some not. Depends on the area.

    It is rare to see a grounding electrode conductor (GEC) terminated in a meter pan any more. Typically this connection is made in the main panel or disconnect.

    Are you saying the electrician put the GEC right under the same terminal as the service neutral? This is a violation and not smart. There should have been a dedicated terminal just for the GEC.
    shader's Avatar
    shader Posts: 235, Reputation: 12
    Full Member
     
    #3

    Jun 29, 2009, 06:29 PM
    Stan, yep that's what he did. The meter pan is old (1966) and my thinking was the same as yours, should have a dedicated terminal for the GEC. Maybe I should just have the whole meter pan replaced as the terminals/interior looks pretty worn... I plan on moving the ground to the disconnect.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Aluminum to Copper ? [ 2 Answers ]

Hello, My mother-in-laws house built in the late 50's has Aluminum wiring throughout. I need to run a new leg ( one-20 amp outlet) from an existing circuit, 20amp AL 12-2/g. Can I do this with copper 12-2/g or need to run new circuit from panel. Also what about GFI outlets on aluminum?

Copper vs aluminum [ 8 Answers ]

I am in the process of building a house and my electrician seems to favor using aluminun wire for some aspects of the house wiring and pushes back when I suggest copper in these instances. First the 200A underground supply cable from the meter to the panel (maybe about 70 feet). He says copper...

Copper or Aluminum wire [ 2 Answers ]

Hi I just replaced my Suncutter Package system with a Goodman Package system. The question is should I replace the (main power supply to AC disconnect) aluminum wire with copper? Thanks Brian

Aluminum or copper? [ 6 Answers ]

My husband and I recently acquired a hot tub. We would like to install every ourselves but are totally green on the subject. So, we have decided to at least purchase the materials and have an electrician just hook it up to the box. What type of wire should we buy. I know it is 6/3 but the hardware...


View more questions Search