    DMoran's Avatar
    DMoran Posts: 9, Reputation: 1
    New Member
     
    #1

    Jun 28, 2009, 09:43 AM
    Trane XL1800 3ton condensing unit
    I've mated a 1991 Rheem Ahu with a 2001 Trane XL1800 Condensing Unit. He condensing unit is dual stage compressors and I have the high side wired to call. I know need to upgrade the ahu and the honeywell chronotherm III t-stat but budget is not allowing it yet. I had a new coil installed with a flat coil 3 years ago. The ahu is in the attic. During the hot part of the day (103 plus) the unit doesn't keep up. The inside temp will rise to 82 plus degrees and will not shut off until later in the evening (10ish). The condensing pressure read low 67ish and the high 210ish drawing about 12.5 amps on both feed leads. I checks the ahu coils and their clean. Any suggestions?

    Thanks
    Daniel
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #2

    Jun 28, 2009, 08:31 PM
    If everything is clean,, coils inside and outside,, the filter clean, you might be charged a little to high with freon
    What does the tag say when running what the amps should be?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #3

    Jun 28, 2009, 11:29 PM
    What was the outside temperature when the gauge said it was 210?
    DMoran's Avatar
    DMoran Posts: 9, Reputation: 1
    New Member
     
    #4

    Jun 29, 2009, 05:53 AM

    The tag only refers to max amps of 22.
    The air temp when I'm having all the cooling issues is over 102.
    DMoran's Avatar
    DMoran Posts: 9, Reputation: 1
    New Member
     
    #5

    Jun 29, 2009, 05:55 AM

    Oh by the way thanks Wmproop and HVAC1000!!
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Jun 29, 2009, 08:07 AM
    210 is low for that outside temp. Looks like you might be low on refrigerant
    DMoran's Avatar
    DMoran Posts: 9, Reputation: 1
    New Member
     
    #7

    Jun 29, 2009, 08:25 AM

    Wouldn't this affect the low side pressures also. Also could there be some restriction in the line causing pressure loss? Don't know that's why I'm asking , Thursday the pressure was high pressure was around 235 and 104 outside. It seems to fluctuate some.
    siberianair's Avatar
    siberianair Posts: 360, Reputation: -4
    Full Member
     
    #8

    Jun 29, 2009, 08:35 AM

    sounds to me like its time to have a certified tech come in... they can watch and monitor the system and find the exact problem. Would need to know superheat and subcool, temps, pressures, splits to know exactly what's wrong.
    but it sounds more like low charge, but without all the variables it is hard to say.
    DMoran's Avatar
    DMoran Posts: 9, Reputation: 1
    New Member
     
    #9

    Jun 29, 2009, 08:54 AM

    Superheat and subcool temps? How would I go about attaining these? I have access to just about all the tools needed . I'm trying to learn something on my own, I have access to ac help of friend and family, but this one I wanted to fix on my own. I don't want to burn up those favors on something I can take care of on my own, its important that I exhaust all my potential first before askinf for there help. Thanks though, you all educating me is much appreciated.
    siberianair's Avatar
    siberianair Posts: 360, Reputation: -4
    Full Member
     
    #10

    Jun 29, 2009, 09:02 AM

    Are you certified to handel refridgerant?
    If not than I can not assist you any further. I do not need to take the chance on a fine or jailtime if for some reason you do not handle the refridgerant properly and something goes wrong.

    Sorry.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Condensing unit not working [ 5 Answers ]

I wanted to know why the contactor is not closing to start the compressor and outdoor fan motor, my indoor fan is coming on.

Wiring a goodman 3ton a/c unit [ 4 Answers ]

I have installed a goodman 3 ton a/c unit and was told I need to install two 30 amp breakers one for heat and one for the a/c. do I run one leg to a/c and one to the heat strips. Thanks

Condensing Unit Fan [ 1 Answers ]

Earlier today my condensing fan worked fine. When I got home on the outside unit the condenser was running but the fan wasn't and the unit was pretty hot and I'm pretty sure it wasn't frorm the sun because the sun usually stops hitting it about 2.5 hrs. from when I noticed this. Any Help would be...

Goodman 3ton split unit Heat will not come on [ 10 Answers ]

After turning up heat, blower will not come on, or the heat. What do I look for or trouble shoot?. thanks

Leaks a/c condensing unit [ 1 Answers ]

There is no charge in my system, it leaked out. I don't have a vaccuum pump, how can I remove the air, could I run some r-22 through the system to chase the air? If so how can I do this. Do the scharder valve o-rings go bad? If so where can I buy them


View more questions Search