    Camper site wire size
    Need to run electric for a camper about 650 feet from my 200 amp service pole at the farm. I need 50 amps for the camper ac and such but I am worried about voltage drop. I am going to run the wire in pvc conduit due to the rocky soil. I can't find any reference to the distance of run relative to the wire size to use. Any help would be great. I really don't want to run a generator.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #2

    Jun 16, 2009, 03:46 PM

    Try using this calculator.Voltage Drop Calculator What voltage is required for the ac?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #3

    Jun 16, 2009, 05:46 PM

    You probably should step up and then back down again for that distance.
    X49's Avatar
    X49 Posts: 3, Reputation: 1
    New Member
     
    #4

    Jun 17, 2009, 01:49 PM
    Thanks for the site, perfect.
    110 volt ac with 13 amp startup 10amp run.

    I don't know about stepup/stepdown. How about more info?
    Thanks
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #5

    Jun 17, 2009, 03:25 PM

    X49, is the ac the only thing you plan to run?
    X49's Avatar
    X49 Posts: 3, Reputation: 1
    New Member
     
    #6

    Jun 18, 2009, 09:23 AM
    My plan is to set one or two travel trailers on site for camping. We have a 30' with one ac now. This one has a 30 amp plug. We will use the site about 10 weekends per year.
    Perhaps in the future I will set another trailer for up and coming grand kids.
    We may set a light to light the area when needed, not full time.
    Thanks
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #7

    Jun 18, 2009, 12:34 PM

    This is really a hard call, but I do believe an electrician should be consulted. I also do believe that 650' is WAY too much for a 3% voltage drop at 120V and the wire cost would be way too expensive.

    A transformer is nearly 100% efficient in converting voltages. Power remains constant. Thus at 1200 V, the current is 1/10 of what's required at 120V. The power company does this all the time.

    It also creates an isolated source and therefore I believe, you don't have to carry the ground or neutral conductors. You'll create them at the other side.

    So, say for instance you use a 240 V to 1200V transformer at the source end and a 1200 V to 240 CT transformer at the other end. The CT becomes ground and your neutral for the other location and your wire size goes down considerably.

    There are better calculators at electrican2.com, but probably won't handle this.

    High voltage it not something you really want to mess with, but you can arrange what you will do with your contractor. e.g. mount boxes, pull cable and bury conduit. He pulls permits ans makes the final connections.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #8

    Jun 18, 2009, 01:56 PM
    650 feet to too long to deliver 120/240 volts.

    Contact an electrician to resolve this, as two transformers of the proper size and voltages are needed for a step-up and step-down installation.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire size & conduit size for 60 am subpanel 150 from source [ 9 Answers ]

Indiana question: I want to install a 60amp subpanel 150 feet from the main panel. This is all exposed runs both inside and out in a commercial envirenement. What gauge and type of copper wire and what size conduit whould I use. How often should insert a junction box in the run. John

Sub Panel AMP Size and Supply Wire Size [ 1 Answers ]

I would like to install a sub panel in my garage I was told to run 6/3 Romex to supply the sub panel and have done so. The run is about 65 feet and I am now wondering after reading this site what is the max I can get for this size wire? I plan to supply a compressor (20 amp) and the garden...

Vintage stove- 3 wire 220v, what size wire? [ 1 Answers ]

We recently purchased a vintage Crosley range. The old wire was a 3-wire 220v, connected to terminals in the back- the black and red wires were actually 6 or so copper strands, and the white was a silver metal. My question is, what amperage do you think I need? Will 10 be enough? Thanks for your...

How to hook up a 4 wire themostat to AC unit on camper [ 1 Answers ]

Yes, I have a coleman AC unit on a 94 wilderness. The colors from the thermostat are black, green, brown, and white. The colors of the wire coming from the AC unit that attaches to the ceiling to the unit are Black, blue, gray, and white. My problem is (oh, I also have a 12 volt wire I don't know...

4 wire home service entrance wire size [ 1 Answers ]

Mobile home requires 4 wire electrical service entrance wire. Distance is 160 foot from meter to breaker panel. 220V service. What size wire do I use? Can I use diff. size for neutral and ground?


View more questions Search