    11yr rheem outdoor unit won't run
    I have a rheem rpka 030jaz units beenworking fine... started to notice it was not cooling...
    Checked outside unit and it wasn't running... I had this probem about two years ago
    Replaced contactor and that fixed problem... so I checked the new one removed cover in points and if I manually press down on conact unit will fire up... so I checked to make sure I was getting the 24v at the contactor it's only reads about 17 -18 v from yellow wire to ground (chassie)... thought maybe thermostat was bad replaced that and still the same just 17v... can anyone lend a helping hand?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jun 15, 2009, 02:31 PM
    Go to both 24 volt terminals on the contactor and see what your reading is. If less that 24 volts or so you have a weak transformer or other low voltage problem. You will need to trace the problem starting at the transformer to see where the voltage drops off. If there are low voltage components in the outside unit like high or low pressure controls they can also cause a low volt problem.
    pwint80's Avatar
    pwint80 Posts: 5, Reputation: 1
    New Member
     
    #3

    Jun 15, 2009, 02:55 PM
    OK it's low v there on both yellow wires... I trace them back to a little browm sq box both yellow wire come out of this box plus a brn on going to the other side of contactor... there's also a larger brn wire that has 24v going into this box... possible this is the relay you speak of... so if 24v going in and only 17v at yellow wie














    Quote Originally Posted by hvac1000 View Post
    Go to both 24 volt terminals on the contactor and see what your reading is. If less that 24 volts or so you have a weak transformer or other low voltage problem. You will need to trace the problem starting at the transformer to see where the voltage drops off. If there are low voltage components in the outside unit like high or low pressure controls they can also cause a low volt problem.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Jun 15, 2009, 08:47 PM
    ((possible this is the relay you speak of))

    Relay? I did not mention a relay in my reply to you I mentioned a contactor.

    ((I trace them back to a little browm sq box))

    I have no idea what this box is or what it does by your description. Is it located inside or outside? Does it have a brand name or part number?

    As I mentioned before you need to trace the problem down to where the voltage is less than 24 volts. This will be the general area where the problem will be located. You might post pictures so there is no misunderstanding the nomenclature of the HVAC descriptions of the part or parts you are talking about.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Old rheem pkg unit [ 2 Answers ]

I have a old rheem package unit with a gas valve that has the thermocouple plugged into a black box that plugs into the gas valve.. . my question is I need help on installing a retro fit kit.. it looks pretty easy but looks like I may have a couple extra wires.. that's where I'm having problems no...

Rheem-heat-pump-outside-unit-humming but blower unit working [ 3 Answers ]

I have a heat pump and ac unit outside. The inside blower fan still working but the outside unit humming. Are there any quick fixes here

RHEEM A/C Unit blower motor won't start [ 5 Answers ]

I have a problem with my RHEEM air package unit Air and heating, the blower motor won't start and it keeps blowing my 24v transformer, transformer literally blows up by doing an explotion noise. Now I am thinking that it might be the blower motor it self the one returnig High Voltage power to my...

Rheem A/C - Older Unit [ 2 Answers ]

How do I find out how old the A/C unit is by the model/serial # and what Seer it is? The unit # is RACB-042JAS. Buying a house and need to determine if A/C is still any good. Thanks

Rheem unit [ 2 Answers ]

Hi can anyone help me I have this rheem unit and now that I turn the heat on the heat pump outside only cames on when I go to the unit and reset the unit by pushing the red buton on the side Thank you


View more questions Search