New Member
|
|
Oct 14, 2006, 09:36 AM
|
|
3 wires out of the wall
I have the Honeywell RTH230B Thermostat. I do not have A/C. I have a gas heated, gravity system. My problem is that I have 3 wires coming out of the wall. Im confused. I am used to themostats having 2 wires. Can anyone help?
|
|
 |
Uber Member
|
|
Oct 14, 2006, 09:57 AM
|
|
What are you trying to do? Ye olde 2 wire thermostats connected a hot wire from the transformer to one side of the gas valve. The Honeywell RTH230B Thermostat will do the same. It will have an RH terminal, connect the hot wire, usually red from the transformer to it. Connect the wire to the gas valve, often white to W or W1. The Honeywell RTH230B Thermostat may require a third wire from the other side of the transformer connected to the B or C terminal. Otherwise, it is not used in your system. If you do not have red and white wires, the wires you do have may be connected to terminals marked R and W at the furnace. Even if you have red and white wires, you might verify where they are connected at the furnace.
I notice some new members here. I hope they know more about the Honeywell RTH230B Thermostat than I do. If so, I may leave these questions to them. I have more to do than get in the way of people that can give better answers than me.
|
|
 |
New Member
|
|
Oct 14, 2006, 10:26 AM
|
|
 Originally Posted by labman
What are you trying to do? Ye olde 2 wire thermostats connected a hot wire from the transformer to one side of the gas valve. The Honeywell RTH230B Thermostat will do the same. It will have an RH terminal, connect the hot wire, usually red from the transformer to it. Connect the wire to the gas valve, often white to W or W1. The Honeywell RTH230B Thermostat may require a third wire from the other side of the transformer connected to the B or C terminal. Otherwise, it is not used in your system. If you do not have red and white wires, the wires you do have may be connected to terminals marked R and W at the furnace. Even if you have red and white wires, you might verify where they are connected at the furnace.
I notice some new members here. I hope they know more about the Honeywell RTH230B Thermostat than I do. If so, I may leave these questions to them. I have more to do than get in the way of people that can give better answers than me.
But I have 3 wires coming from the wall. After I connect the power supply an the heating signal wire where does the 3rd wire go?
|
|
 |
Uber Member
|
|
Oct 14, 2006, 12:26 PM
|
|
''The Honeywell RTH230B Thermostat may require a third wire from the other side of the transformer connected to the B or C terminal. Otherwise, it is not used in your system.''
If you don't have A/C or a blower for the furnace, it doesn't need the third wire. If the thermostat doesn't need a third wire, leave it unconnected.
|
|
 |
Ultra Member
|
|
Oct 14, 2006, 02:48 PM
|
|
 Originally Posted by luvinaj
I have the Honeywell RTH230B Thermostat. I do not have A/C. I have a gas heated, gravity system. My problem is that I have 3 wires coming out of the wall. Im confused. I am used to themostats haveing 2 wires. Can anyone help?
I'm not sure of the 3rd wire either. You need to find out where each of these 3 wires go on the furnace. Old gravity furnace means there is not a blower motor, thusly the air moves by the rise and fall of hot and cold air. Many of the old gravity furnaces also have no transformer, instead they use a powerpile to supply the voltage and a millivolt thermostat "must" be used.
|
|
 |
New Member
|
|
Oct 14, 2006, 09:57 PM
|
|
 Originally Posted by labman
''The Honeywell RTH230B Thermostat may require a third wire from the other side of the transformer connected to the B or C terminal. Otherwise, it is not used in your system.''
If you don't have A/C or a blower for the furnace, it doesn't need the third wire. If the thermostat doesn't need a third wire, leave it unconnected.
I did leave the 3rd wire unconnected an the stat works perfectly thank you guy
|
|
 |
New Member
|
|
Oct 20, 2006, 11:17 AM
|
|
Comment on labman's post
The answer was just what I was looking for, Thanks
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
3 wires + 2 wires POOL MOTOR
[ 2 Answers ]
I need help connecting a motor for my pool.
The motor has 3 wires coming out of it. 1 white, 1 black, 1 black with a white stripe. A continuity test on the 2 blacks says they are wired together somewhere.
I have a power cable coming out of the ground. 1 white + 1 black cables inside. ...
Installing Ceiling Fan Wall Remote with Red & Black Wires?
[ 13 Answers ]
I am trying to install a Hampton Bay Wall Remote Control that transmits a signal to a receiver that I will install behind the Ceiling Fan assembly.
Problem: Remote instructions state to connect the 2 Black wires from the wall switch to the new Remote switch. The wall switch has a Red and a...
Help - What to do with the Grounding Wires
[ 5 Answers ]
Because of brown waters, I want to re-run the hot/cold water pipes for the entire house. But there is one major problem, the existing galvanized pipes had some grounding wires attached to them and I'll plan to use the PEX pipe. I have no ideas how to run the new grounding wires when I take out...
Birds on Wires
[ 1 Answers ]
Could you please explain how birds can sit on electrical wires without being harmed? My 7 year old son asked me this and I cannot answer him!
Hampton Bay remote wires do not match fan wires
[ 1 Answers ]
Yesterday I installed a new Hunter ceiling fan. I also purchased a Hampton Bay wireless wall switch. Everything went well until I wired up the remote receiver. The receiver has a blue wire for the light that is supposed to connect to the blue wire (light) from the fan. The Hunter fan does not have...
View more questions
Search
|