    diehl2008's Avatar
    diehl2008 Posts: 23, Reputation: 1
    New Member
     
    #1

    Jun 10, 2009, 07:06 AM
    AC Compressor and Fan off
    If I set the thermostat to below the room temperature the fan which is set in auto mode will start working, but if I go outside and look the AC unit, it is dead... neither the fan or the compressor work! I have turned the breaker for the unit ON, OFF... but nothing happened. I am trying to find out if there might be a fuse or breaker in the heater or something. The weird part is that is blowing air but I guess because is coming from the heater.

    Any help is greatly appreciate it!
    diehl2008's Avatar
    diehl2008 Posts: 23, Reputation: 1
    New Member
     
    #2

    Jun 10, 2009, 07:21 AM

    I also want to mention that this was working during the day but I decided to turn it off instead of letting it go into a higher temp and when I turn it back on the fan and the compressor didn't turn on at all.
    dac122's Avatar
    dac122 Posts: 463, Reputation: 17
    Full Member
     
    #3

    Jun 10, 2009, 09:54 AM

    Your indoor air handler and furnace are on separate circuits from the outdoor unit, so, yes, you blower will run independent of whether the outdoor unit works.

    You need to determine why the outdoor unit is not coming on.
    diehl2008's Avatar
    diehl2008 Posts: 23, Reputation: 1
    New Member
     
    #4

    Jun 10, 2009, 10:16 AM
    I noticed that there is a breaker right beside the unit. Maybe when I turn the AC off turn off a breaker or something? I don't know what to check first.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #5

    Jun 10, 2009, 12:58 PM
    Since the system was working before you turned it off, perhaps the problem is in the thermostat. If the selector switches are of the slide type, try moving them back and forth a few times.
    diehl2008's Avatar
    diehl2008 Posts: 23, Reputation: 1
    New Member
     
    #6

    Jun 10, 2009, 01:20 PM
    Well the thing is that is digital, I removed it and made sure all the connections were seating properly but everything looked okay.
    dac122's Avatar
    dac122 Posts: 463, Reputation: 17
    Full Member
     
    #7

    Jun 10, 2009, 01:33 PM

    If you have reset power at the air handler, outdoor unit and are relatively certain there is power, or have no other way to determine, you have to break out a voltmeter and start testing power to see where the problem is.
    diehl2008's Avatar
    diehl2008 Posts: 23, Reputation: 1
    New Member
     
    #8

    Jun 10, 2009, 02:07 PM
    I haven't reset the power or the breaker on the outside unit yet. Once I get back home in a an hour I will try that to see if that works. Hopefully that fixes the problem.
    Thanks to all for your responses :-).
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #9

    Jun 10, 2009, 03:43 PM

    Most likely your problem is breaker outside, there may also be some fuses located in breaker outside. Do you here any slight hum at all at outside unit? If you do, this noise is the contactor being pulled in, which means unit is calling for cooling, but there is no power there to make it run. Please let me know if you hear anything at all.
    diehl2008's Avatar
    diehl2008 Posts: 23, Reputation: 1
    New Member
     
    #10

    Jun 10, 2009, 03:43 PM
    I tried the pull fuse from outside of the AC Unit, also I can hear the power go of the compressor but the fan is completely dead. Can also hear the clutch oncce in awhile.
    Could this be a compressor failure?
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #11

    Jun 10, 2009, 03:57 PM

    Are you saying compressor is running, fan is not, and what do you mean by clutch? I find that a lot of time I use different terminology than others, so I just want to make sure exactly what is happening to better assist you.
    diehl2008's Avatar
    diehl2008 Posts: 23, Reputation: 1
    New Member
     
    #12

    Jun 10, 2009, 04:02 PM

    Oh no problem, thanks for helping me out with this issue.
    The compressor is humming and the fan doesn't turn on but you can hear a click like every 5 minutes.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #13

    Jun 10, 2009, 05:31 PM

    The cluch you are hearing is probably the compressor valving out due to high head pressure
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #14

    Jun 10, 2009, 05:31 PM
    Does your unit have 2 capasitors or one outside in the units electric pannel?


    http://img.diytrade.com/cdimg/377701..._Capacitor.jpg

    Or


    http://img.diytrade.com/cdimg/377701...itor_CBB65.jpg
    diehl2008's Avatar
    diehl2008 Posts: 23, Reputation: 1
    New Member
     
    #15

    Jun 10, 2009, 06:05 PM
    Only one, I don't see a capacitor outside
    diehl2008's Avatar
    diehl2008 Posts: 23, Reputation: 1
    New Member
     
    #16

    Jun 11, 2009, 08:23 AM
    So do you guys have any other ideas of what can be causing this issue?

    - Furnace fan blowing when AC on.
    - From the AC Unit outside you can hear a hum coming out of the compressor and you can hear a click coming out of it once in awhile.
    - The Fan of the AC Unit is not moving at all.

    Is there any possibilities that this could be a motor problem?
    The compressor seems to be working but cold air is not moving due to the fan not working.
    dac122's Avatar
    dac122 Posts: 463, Reputation: 17
    Full Member
     
    #17

    Jun 11, 2009, 08:49 AM

    You are close to the problem. You need to get power to that fan, so check the capacitor, contactor and any wiring to the fan motor. If all checks out you may have a bad fan motor.
    diehl2008's Avatar
    diehl2008 Posts: 23, Reputation: 1
    New Member
     
    #18

    Jun 11, 2009, 09:14 AM
    Is there a way to test the capacitor without a multimeter?
    How can I make sure the motor(fan) its not working?
    Apparently the Capacitor can give an extra voltage jolt to get the hard-starting motor spinning, right?
    So it could be like you said the capacitor.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #19

    Jun 11, 2009, 03:15 PM

    If you don't have a multimeter, just take the capacitor down to any heating and cooling company and they should be able to test it for you free of charge.
    diehl2008's Avatar
    diehl2008 Posts: 23, Reputation: 1
    New Member
     
    #20

    Jun 11, 2009, 03:40 PM

    I may sound desperate but I tried to move the fan using a screwdriver and started moving at normal speed, but now the problem is that it's not blowing cold air I still can hear the compressor making noise but it's sounding like a refrigerator if that makes sense? Please advice

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Air Compressor doesn't run [ 10 Answers ]

I have 4 year old husky air compressor that quit working. I thought the motor burned up so took it in to have fixed, hooked up power and worked fine. The guy says it's my power source. It's a 240v motor 15 amp wired directly to my panel with separate breakers. I have 119 volts at each wire through...

Air compressor [ 1 Answers ]

1a/ a rotary air compressor increases the absolute pressure of the air from 100 kNm-2 to 230 kNmm-2 and the specific volume of the air is reduced from 0.7m3 kg-1 to 0.46 m3 kg-1. If the internal energy of the air is increased by 40 kj kg-1 find the change in enthalpy of 8 kg of air. b/ If at...

AC Compressor [ 2 Answers ]

The AC unit in my house is 25 years old, and it's not big enough for the size of our house, it is also not very energy efficient. We have a home warranty that we got when we bought our house and it’s due to expire in a couple of months. Is there something we can do to “break” the compressor so the...

Compressor [ 2 Answers ]

Hey we were out of town then came back and the ac breaker was tripped after turning on the fans run but the compressoe never kicks in we never had any problems with this unit before can some one give us some ideas were to start thanks:D


View more questions Search