    Read the previous thread by PB21 but decided to start a new one as I have the boat house, but house is coming later.

    I'm finishing boat house and I want to pull service wire through electrical conduit (2") I installed underneath that is stubbed out to a storage room under the staircase which is where I plan to put a sub panel.

    I will have:

    2 boat lifts rated 30 amp each
    Water pump 30 amp start up
    12 outlets, battery chargers, small appliances, fridge, TV, stereo etc.
    Security and other misc. lights.
    Plan to add a 3rd personal h2o craft lift in future.

    Questions:

    1. What size panel, type?

    2. What size service wire? Plan to run direct bury starting 5' behind seawall. Run will be somewhere around 200'-250' to house.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jun 7, 2009, 06:22 AM
    I guess with 78 views of this post, your wondering why still no answer.

    You can do your own voltage drop calculations here:

    Voltage Drop Calculator

    Long distance feeders are a problem, esp trying to deliver 120/240 volts this distance of 200 to 250 feet.

    First off, 50 foot difference is too much, provide one distance that is accurate.

    Sizing the ampacity of the panel is a problem, as we need to know more detail from the list of loads you provide, and what would be the max load in amps at any one time.

    The size panel is somewhat irrelevant until the max load is determined.

    I suspect that a 100 amp panel and feeder will be fine.

    However to size the feeder conductor is the issue to insure there is 120/240 volts +/- 3 % at the panel with such a long feeder.

    The amount of voltage drop will be completely dependent on the max amp load.

    You have 2 in conduit to deal with, which should be large enough.

    What do you want to use, copper or aluminum wire? Copper wire can be smaller than aluminum, but you need to be ready to afford to purchase this length of wire. Aluminum is cheaper, will need to be larger compared to the same ampacity copper wire.

    What is the voltage of the loads?

    Using the calculator I provided, you can enter assumptions of the various data.

    For example, if you need 30 amps of 120 volt loads,which I think is a reasonable assumption, at 250 feet, you will see that #1/0 aluminum will be needed.

    This brings up another issue. If you use a 100 amp rated panel, the termination connectors will not be large enough to handle the large wire needed to reduce the voltage drop, so some method of reducing wire size at both ends will be needed.

    Or you can use a 200 amp rated panel, will have larger wire connectors to accept the larger wire feeder, and protect it with a 100 amp breaker.

    First need to make a decision on what the max load amps at what voltage to begin sizing this long feeder.



    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Jun 7, 2009, 07:30 AM
    Quote Originally Posted by Blueforester View Post

    I'm finishing boat house and I want to go ahead and pull service wire through electrical conduit (2") I installed underneath that is stubbed out to a storage room under the staircase which is where I plan to put a sub panel.

    I will have:

    2 boat lifts rated 30 amp each
    water pump 30 amp start up
    12 outlets, battery chargers, small appliances, fridge, TV, stereo etc.
    Security and other misc. lights.
    Plan to add a 3rd personal h2o craft lift in future.
    I know I will get flamed for this, but I have to ask.

    With all this, money is obviously not an issue. Why not just hire an electrician to come in and do the job right?
    Blueforester's Avatar
    Blueforester Posts: 19, Reputation: 1
    New Member
     
    #4

    Jun 9, 2009, 08:13 AM

    [/QUOTE]

    Quote Originally Posted by tkrussell View Post
    I guess with 78 views of this post, your wondering why still no answer.
    Thanks for reply. I was beginning to think I stumped the panel.

    You can do your own voltage drop calculations here:

    Voltage Drop Calculator

    Long distance feeders are a problem, esp trying to deliver 120/240 volts this distance of 200 to 250 feet.

    First off, 50 foot difference is too much, provide one distance that is accurate.

    Currently working on site plan. Actually, roughly figuring I can probably reach w/ 142'

    Sizing the ampacity of the panel is a problem, as we need to know more detail from the list of loads you provide, and what would be the max load in amps at any one time.

    It is unlikely that both lifts, water pump, battery chargers and blenders etc. will all be on at the same time. My concern is having enough power available in case someone flushes the head while I'm raising my boat and the fridge comes on when someone is grabbing a beer out of the fridge!

    The size panel is somewhat irrelevant until the max load is determined.

    I suspect that a 100 amp panel and feeder will be fine.

    What I was thinking about installing

    However to size the feeder conductor is the issue to insure there is 120/240 volts +/- 3 % at the panel with such a long feeder.

    The amount of voltage drop will be completely dependent on the max amp load.

    You have 2 in conduit to deal with, which should be large enough.

    What do you want to use, copper or aluminum wire? Copper wire can be smaller than aluminum, but you need to be ready to afford to purchase this length of wire. Aluminum is cheaper, will need to be larger compared to the same ampacity copper wire.

    No preference. Which ever cost the least. It all works the same in end. I like the idea of running aluminum for the main run and tie in copper at junction boxes at the house and bank/seawall where the conduit is currently stubbed out

    What is the voltage of the loads?

    Everything is 120v except water pump which is 240v.


    Using the calculator I provided, you can enter assumptions of the various data.

    For example, if you need 30 amps of 120 volt loads,which I think is a reasonable assumption, at 250 feet, you will see that #1/0 aluminum will be needed.

    This brings up another issue. If you use a 100 amp rated panel, the termination connectors will not be large enough to handle the large wire needed to reduce the voltage drop, so some method of reducing wire size at both ends will be needed.

    Or you can use a 200 amp rated panel, will have larger wire connectors to accept the larger wire feeder, and protect it with a 100 amp breaker.

    First need to make a decision on what the max load amps at what voltage to begin sizing this long feeder.

    I'm almost certain max load will be < 100amps. I would rather have a little more than not enough.


    I guess I do not have the specific information as I have not started the house yet.

    Quote Originally Posted by tkrussell View Post
    I guess with 78 views of this post, your wondering why still no answer.
    Thanks for reply. I was beginning to think I stumped the panel.

    You can do your own voltage drop calculations here:

    Voltage Drop Calculator

    Long distance feeders are a problem, esp trying to deliver 120/240 volts this distance of 200 to 250 feet.

    First off, 50 foot difference is too much, provide one distance that is accurate.

    Currently working on site plan. Actually, roughly figuring I can probably reach w/ 142'

    Sizing the ampacity of the panel is a problem, as we need to know more detail from the list of loads you provide, and what would be the max load in amps at any one time.

    It is unlikely that both lifts, water pump, battery chargers and blenders etc. will all be on at the same time. My concern is having enough power available incase someone flushes the head while I'm raising my boat and the fridge comes on when someone is grabbing a beer out of the fridge!

    The size panel is somewhat irrelevant until the max load is determined.

    I suspect that a 100 amp panel and feeder will be fine.

    What I was thinking about installing

    However to size the feeder conductor is the issue to insure there is 120/240 volts +/- 3 % at the panel with such a long feeder.

    The amount of voltage drop will be completely dependent on the max amp load.

    You have 2 in conduit to deal with, which should be large enough.

    What do you want to use, copper or aluminum wire? Copper wire can be smaller than aluminum, but you need to be ready to afford to purchase this length of wire. Aluminum is cheaper, will need to be larger compared to the same ampacity copper wire.

    No preference. Which ever cost the least. It all works the same in end. I like the idea of running aluminum for the main run and tie in copper at junction boxes at the house and bank/seawall where the conduit is currently stubbed out

    What is the voltage of the loads?

    Everything is 120v except water pump which is 240v.


    Using the calculator I provided, you can enter assumptions of the various data.

    For example, if you need 30 amps of 120 volt loads,which I think is a reasonable assumption, at 250 feet, you will see that #1/0 aluminum will be needed.

    This brings up another issue. if you use a 100 amp rated panel, the termination connectors will not be large enough to handle the large wire needed to reduce the voltage drop, so some method of reducing wire size at both ends will be needed.

    Or you can use a 200 amp rated panel, will have larger wire connectors to accept the larger wire feeder, and protect it with a 100 amp breaker.

    First need to make a decision on what the max load amps at what voltage to begin sizing this long feeder.

    I'm almost certain max load will be < 100amps. I would rather have a little more than not enough.


    I guess I do not have the specific information as I have not started the house yet.


    Blueforester's Avatar
    Blueforester Posts: 19, Reputation: 1
    New Member
     
    #5

    Jun 9, 2009, 08:22 AM
    The last post did not work as planned! Let me try again.


    Originally Posted by tkrussell
    I guess with 78 views of this post, your wondering why still no answer.


    Thanks for reply. I was beginning to think I stumped the panel.

    You can do your own voltage drop calculations here:

    Voltage Drop Calculator

    Long distance feeders are a problem, esp trying to deliver 120/240 volts this distance of 200 to 250 feet.

    First off, 50 foot difference is too much, provide one distance that is accurate.

    Currently working on site plan. Actually, roughly figuring I can probably reach w/ 142'

    Sizing the ampacity of the panel is a problem, as we need to know more detail from the list of loads you provide, and what would be the max load in amps at any one time.

    It is unlikely that both lifts, water pump, battery chargers and blenders etc. will all be on at the same time. My concern is having enough power available incase someone flushes the head while I'm raising my boat and the fridge comes on when someone is grabbing a beer out of the fridge!

    The size panel is somewhat irrelevant until the max load is determined.

    I suspect that a 100 amp panel and feeder will be fine.

    What I was thinking about installing

    However to size the feeder conductor is the issue to insure there is 120/240 volts +/- 3 % at the panel with such a long feeder.

    The amount of voltage drop will be completely dependent on the max amp load.

    You have 2 in conduit to deal with, which should be large enough.

    What do you want to use, copper or aluminum wire? Copper wire can be smaller than aluminum, but you need to be ready to afford to purchase this length of wire. Aluminum is cheaper, will need to be larger compared to the same ampacity copper wire.

    No preference. Which ever cost the least. It all works the same in end. I like the idea of running aluminum for the main run and tie in copper at junction boxes at the house and bank/seawall where the conduit is currently stubbed out

    What is the voltage of the loads?

    Everything is 120v except water pump which is 240v.

    Using the calculator I provided, you can enter assumptions of the various data.

    For example, if you need 30 amps of 120 volt loads,which I think is a reasonable assumption, at 250 feet, you will see that #1/0 aluminum will be needed.

    This brings up another issue. If you use a 100 amp rated panel, the termination connectors will not be large enough to handle the large wire needed to reduce the voltage drop, so some method of reducing wire size at both ends will be needed.

    Or you can use a 200 amp rated panel, will have larger wire connectors to accept the larger wire feeder, and protect it with a 100 amp breaker.

    First need to make a decision on what the max load amps at what voltage to begin sizing this long feeder.

    I'm almost certain max load will be < 100amps. I would rather have a little more than not enough.

    I guess I do not have the specific information as I have not started the house yet.
    Blueforester's Avatar
    Blueforester Posts: 19, Reputation: 1
    New Member
     
    #6

    Jun 9, 2009, 08:41 AM
    Quote Originally Posted by stanfortyman View Post
    I know I will get flamed for this, but I have to ask.

    With all this, money is obviously not an issue. Why not just hire an electrician to come in and do the job right?
    That's not a flame, but rather a good question. My wife ask me the same thing all the time. I'm a hardcore DIY. Do not mind doing the work, enjoy doing the work. But to your point, I'm confident I can "do it right." I'm seeking a good solution. I'm finishing up the major construction of the boat house and the wiring phase is coming up quickly. I ran across this website doing a little research and thought I would try it out. Reading through some of the post there are several that respond here that I can tell are actually very knowledgeable on this subject
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #7

    Jun 9, 2009, 01:11 PM
    Then I recommend you pull 3 #4/0 XHHW Aluminum for the two hots and one neutral and 1 #2 XHHW Al for the green equipment ground, use a 200 Amp rated panel and feed it with a 100 amp breaker at the main distribution point.

    At the main #2 wire will need to be used to extend and reduce the #4/0 because it will not fit in the new 100 amp breaker.
    Blueforester's Avatar
    Blueforester Posts: 19, Reputation: 1
    New Member
     
    #8

    Jun 9, 2009, 01:53 PM
    Thanks! I think that is a great solution. I plan to install panel so I can begin running wiring for fixtures and make the connection for the water pump. I will probably pull service wire to panel and coil up the rest. When I get the site work started I plan to trench for utilities and lay in the serice line to the main at the house. As part of the electrical plan for my house I will include setting a 100 amp breaker at the main and making the reduction and connection.

    Thanks again!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Best way to run electrical to residential boat pier? [ 4 Answers ]

I am wondering if anyone has any experience with wiring up a residential boat pier? Im not sure if its best to install a weatherproof sub panel at the end of the pier and then come out of it with all of the associated loads such as 240 v twistlock, 120 v gfci outlet, lighting, boat lift power and...

Going from 150 amp to 200 amp electrical service? [ 1 Answers ]

Hi out there, My names Bill and I'd like to know what exactly is involved in changing from a 150 amp To a 200 amp electrical service? At the moment I have a 150 amp service and would like to upgrade. Does the meter socket box and feed wiring have to be changed? ...

Proper GFI setup for boat house [ 2 Answers ]

I am running electricity to my floating boat house. Right now I have a 50 amp breaker box on "land" I will run 6/3 wire to my dock. My intention is then to run the power to a circuit breaker panel located on the boat house using 6/3 wire(already installed). From each circuit on the panel I wanted...

Changing from metered service on my shop to service from my house. [ 2 Answers ]

I’ve had the meter and 3 wire service cable removed from my shop. I’ve purchased 90 feet of 100 amp direct burial cable to run from the lower section of my home meter to my shop. Not being an electrician, I’m still trying to install this changeover. The direct burial cable has 4 wires. 2 larger...

My boat and dock where destroyed by neighbors broken loose boat during hurricane [ 3 Answers ]

As I said above, during hurricane Wilma my neighbors boat broke loose from its mooring and floated down to my dock, two homes away, and proceeded to smash my boat and dock until the storm was over. My dock was destroyed and my boat was knocked off the lift and sank, Do I have any recourse, as my...


View more questions Search