    20 amp breaker to 30 amp breaker
    I just put window air conditioners in my boys bedrooms. The 20 amp breaker that the two rooms are using keeps tripping. Will installing a 30 amp breaker solve the problem?
    andrewc24301's Avatar
    andrewc24301 Posts: 374, Reputation: 29
    Full Member
     
    #2

    Jun 7, 2009, 08:41 PM

    Nope, that would create a fire hazard, the 20 amp breaker is tripping because the circuit is being overloaded. Installing a higher amperage breaker would defeat the safety.

    You might try having an electrician run a dedicated circuit for each unit if they are pulling that much of a load.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #3

    Jun 8, 2009, 07:32 AM

    You must know the gauge of the wires on this circuit to give a definitive answer. In all likelihood it would be a fire hazard since electricians would not use a wire heavier than 12 gauge for a 20 amp breaker. This chart should help you understand the correct relationship between wire gauge and breaker size. Wire sizes, gauges, for breakers
    wiringgenius's Avatar
    wiringgenius Posts: 11, Reputation: 1
    New Member
     
    #4

    Jun 11, 2009, 07:36 AM
    An Air Con system will generally pull 3 times the current on start up, This can be overcome by fitting a type D breaker which is designed to absorb this start up current. Never just put a bigger ampage of breaker in as this will only make any fault go away until the fault is big enough to trip the bigger one but if the wiring can't take it then it will be too late.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    Jun 11, 2009, 08:02 AM
    Wiring genius, type D breaker is not used in North America in standard residential wiring.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Gfci breaker + outlet in same circuit.breaker tripping [ 4 Answers ]

I have a gfci breaker for a bathroom and there is an additional gfci outlet in the bathroom on the same circuit. The breaker was tripping intermittently over the past week and now will not re-engage. Should I suspect a faulty breaker or is it better to troubleshoot the circuit first? The...

How do I determine breaker amps on a 240v double breaker? [ 7 Answers ]

Hi, I have a new elec. Cooktop that needs 240V, 40 amps. Each pole of the double pole breaker for my cooktop circuit Says 30amps. So can this 240v circuit support 60 amps, or just 30? Thanks!

Bathroom GFI outlet trips breaker at breaker panel [ 2 Answers ]

Hello all. Our house is approximately 13 years old. Each morning when both the iron and blow dryer is plugged into two separate GFI outlets in the master bathroom, the circuit will trip the 15 amp breaker in the breaker panel. Is it possible to upgrade the breaker to a 20 amp without...

Replacing GFCI Breaker With A Regular Breaker [ 1 Answers ]

I have a 15 amp circuit serving only a single outlet on my deck. It is protected by a GFCI circuit breaker in the home's single 125 amp service panel. I wish to replace the GFCI breaker with a regular 15 amp GE breaker. I will then protect the circuit with a GFCI outlet. I am familiar with...

Replacing Circuit Breaker with Higher AMP Breaker [ 8 Answers ]

Excuse me, I did look at the code book as is suggested in your Sticky. The NFPA may answer this question, but I am not knowledgeable enough to recognize it: Our offices are upstairs in an older (renovated home) building with modern wiring. We have 4 computers, 3 printers, and miscellaneous with...


View more questions Search