    nelsonesp Posts: 3, Reputation: 1
    New Member
     
    #1

    May 20, 2009, 10:13 PM
    My AC keeps blowin fuce on the control board
    5 amp fuce keeps blowin on the contol board in my AC furnace, went Itryed to put the AC on
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #2

    May 21, 2009, 10:03 AM
    You have a short somewhere ,check the tstat wires make sure the wires arn`t frayed or touching anywhere, especially from the furnace to the outside ac unit, if nothing maybe take the tstat wires loose from the contactor and try again,, could be a shorted out contactor in ac unit,, let us know what you`ve found
    jerro's Avatar
    jerro Posts: 172, Reputation: 5
    Junior Member
     
    #3

    May 21, 2009, 10:54 AM

    Is this the first time you've tried turning it on this year? Sounds like your control board has shorted out. Did you any lightning strikes in your area lately?
    nelsonesp's Avatar
    nelsonesp Posts: 3, Reputation: 1
    New Member
     
    #4

    May 21, 2009, 01:31 PM
    Quote Originally Posted by wmproop View Post
    you have a short somewhere ,check the tstat wires make sure the wires arn`t frayed or touching anywhere,,especialy from the furnace to the outside ac unit,,if nothing maybe take the tstat wires loose from the contactor and try again,,,,could be a shorted out contactor in ac unit,,,,,let us know what you`ve found
    Tnx to all , I fix the problem , it was the transform. Million tnks
    thePard's Avatar
    thePard Posts: 7, Reputation: 1
    New Member
     
    #5

    May 21, 2009, 05:54 PM
    I just had the same problem in an older furnace... with a newer AC unit.
    Unfortunately, it doesn't have a fuse on the 24 volt supply that runs the
    Compressor contactor (relay)... There is not even a circuit board.
    So it burned out the 24 volt transformer/fan relay

    There was a funny stink, like shellac burning in the basement.. and the same smell
    In the access panel where the burners are located...

    I replaced the 24 volt supply/relay and then found out that the AC still did not turn on
    From the t-stat... in fact when I turned the control to cool, the furnace fan stopped running because the 24 volts was shorted out by the compressor contactor/relay.

    I quickly turned off the cooling switch at the t-stat and went outside to look at the contactor...
    The compressor started when I depressed the manual switch on the contactor.

    I will be replacing the contactor since that is where the short is located.
    Yes, the AC unit is a Goodman and the contactor is a GE part.

    A fuse in the 24 volt circuit would have saved me $50 for the fan relay power supply.

    I bet this never happens to me again, so I thought I would pass it on

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bad control board [ 13 Answers ]

We have an older Trane gas furnace (TUC series) and the control board went bad (model 50e47-060). The furnace would come on, but there was no signal to the ignitor per the technician who wanted to charge almost $1K to replace the control board. With money being so tight, we purchased a new board on...

Control board replacement [ 2 Answers ]

I am replacing a control board in a bryant 395cav heater the old one was missing, perhaps taken by the last resident, anyhow, I got a new ceso110057-02 fixed speed furnace control replacement kit but have no idea which wires connect to which spade plugs on the board, I hope someone can enlighten me...

Control board [ 4 Answers ]

I'm working on a forced hot air furnace that's in a basement that got flooded and the furnace was only on 2-4 so it looks like the whole blower motor and control board transformer got flooded. I responded to a no heat call today check the unit the unit won't do nothing, it has power coming from...

Control board [ 1 Answers ]

My control board seems to not be working the light won't come on it is a goodman 90% furnace I do not have the home owners book for it

Can I install a fan control board? [ 3 Answers ]

I am a broke, but resourceful guy who got a quote from an HVAC company to install a new fan control board in my Ducan furance for $420. He wrote to part numbers on the estimate. Ducane part 20430801 (Ducane) & ST9160B1076 (Honeywell). He told me it would take him 1-1.5 hrs to install. To make...


View more questions Search