5 amp fuce keeps blowin on the contol board in my AC furnace, went Itryed to put the AC on
|
|
 |
Ultra Member
|
|
May 21, 2009, 10:03 AM
|
|
You have a short somewhere ,check the tstat wires make sure the wires arn`t frayed or touching anywhere, especially from the furnace to the outside ac unit, if nothing maybe take the tstat wires loose from the contactor and try again,, could be a shorted out contactor in ac unit,, let us know what you`ve found
|
|
 |
Junior Member
|
|
May 21, 2009, 10:54 AM
|
|
Is this the first time you've tried turning it on this year? Sounds like your control board has shorted out. Did you any lightning strikes in your area lately?
|
|
 |
New Member
|
|
May 21, 2009, 01:31 PM
|
|
 Originally Posted by wmproop
you have a short somewhere ,check the tstat wires make sure the wires arn`t frayed or touching anywhere,,especialy from the furnace to the outside ac unit,,if nothing maybe take the tstat wires loose from the contactor and try again,,,,could be a shorted out contactor in ac unit,,,,,let us know what you`ve found
Tnx to all , I fix the problem , it was the transform. Million tnks
|
|
 |
New Member
|
|
May 21, 2009, 05:54 PM
|
|
I just had the same problem in an older furnace... with a newer AC unit.
Unfortunately, it doesn't have a fuse on the 24 volt supply that runs the
Compressor contactor (relay)... There is not even a circuit board.
So it burned out the 24 volt transformer/fan relay
There was a funny stink, like shellac burning in the basement.. and the same smell
In the access panel where the burners are located...
I replaced the 24 volt supply/relay and then found out that the AC still did not turn on
From the t-stat... in fact when I turned the control to cool, the furnace fan stopped running because the 24 volts was shorted out by the compressor contactor/relay.
I quickly turned off the cooling switch at the t-stat and went outside to look at the contactor...
The compressor started when I depressed the manual switch on the contactor.
I will be replacing the contactor since that is where the short is located.
Yes, the AC unit is a Goodman and the contactor is a GE part.
A fuse in the 24 volt circuit would have saved me $50 for the fan relay power supply.
I bet this never happens to me again, so I thought I would pass it on
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Bad control board
[ 13 Answers ]
We have an older Trane gas furnace (TUC series) and the control board went bad (model 50e47-060). The furnace would come on, but there was no signal to the ignitor per the technician who wanted to charge almost $1K to replace the control board. With money being so tight, we purchased a new board on...
Control board replacement
[ 2 Answers ]
I am replacing a control board in a bryant 395cav heater the old one was missing, perhaps taken by the last resident, anyhow, I got a new ceso110057-02 fixed speed furnace control replacement kit but have no idea which wires connect to which spade plugs on the board, I hope someone can enlighten me...
Control board
[ 4 Answers ]
I'm working on a forced hot air furnace that's in a basement that got flooded and the furnace was only on 2-4 so it looks like the whole blower motor and control board transformer got flooded. I responded to a no heat call today check the unit the unit won't do nothing, it has power coming from...
Control board
[ 1 Answers ]
My control board seems to not be working the light won't come on it is a goodman 90% furnace I do not have the home owners book for it
Can I install a fan control board?
[ 3 Answers ]
I am a broke, but resourceful guy who got a quote from an HVAC company to install a new fan control board in my Ducan furance for $420. He wrote to part numbers on the estimate. Ducane part 20430801 (Ducane) & ST9160B1076 (Honeywell). He told me it would take him 1-1.5 hrs to install.
To make...
View more questions
Search
|