    Thermostat wiring messed up
    Hello all: Yesterday, I tried to replace my old thermostat with a Honeywell Digital Thermostat. After I labeled the wires and connected them to the new thermostat, nothing worked so I quickly reinstalled my old mercury thermostat but nothing works there either. I accidentally touched all the wires together ( didn't know I was not supposed to do this). Is that the problem? What can I do to get the old (or the new) thermostat working?

    Robert
    rickdb1's Avatar
    rickdb1 Posts: 185, Reputation: 15
    Junior Member
     
    #2

    Oct 1, 2006, 04:46 AM
    You shorted out the transformer in the furnace. It will need to be replaced. Always turn the power off at the furnace when working on it...
    mltascp's Avatar
    mltascp Posts: 6, Reputation: 1
    New Member
     
    #3

    Oct 1, 2006, 05:17 AM
    Does home depot or Lowe's carry these transformers? By the way, thanks for the quick reply.

    Robert
    esquire1's Avatar
    esquire1 Posts: 2,483, Reputation: 209
    Ultra Member
     
    #4

    Oct 1, 2006, 06:06 AM
    Never seen one at Lowe's or Home Depot. Probably need to go to HVAC supply house. I do think I have seen them at Radio Shack. Just be sure to replace with the right one though. If you have a volt meter and are careful work with electricity, you can verify if you have 24V coming out of the transformer. If you have a circuit board in airhandler you may have on popped the 3 amp fuse in it. I have been lucky in the past and have found that that was the only problem
    mltascp's Avatar
    mltascp Posts: 6, Reputation: 1
    New Member
     
    #5

    Oct 1, 2006, 06:13 AM
    My thermostat says "24 VAC Heat Pump Thermostat" so it is 24 volt transformer. I looked inside the circuit board of the handler and I could not find anything resembling a fuse. Do you know what it looks like?
    esquire1's Avatar
    esquire1 Posts: 2,483, Reputation: 209
    Ultra Member
     
    #6

    Oct 1, 2006, 06:39 AM
    If you have a circuit board, normally they are near the bottom of it. It is a 3 amp fuse, looks (and is) the mini auto fuse. If you have a volt meter verify if you have 24 V on the low voltage side of transforme.ie. You have 120 volts coming into transformer and 24V coming out. If you have an older unit you will not have a circuit board
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #7

    Oct 1, 2006, 06:43 AM
    Also be sure the power rating of a replacement transformer meets or exceeds the rating of the existing transformer. Transformers are rated in VA (volt-amps), and the transformer should be rated as a "control transformer".

    My point is not just any 24 volt transformer can be used.

    Can you find a wiring diagram for you unit? Either published in the manual, and/or pasted on the inside door of the unit? If you can find this, and know how to read wiring digrams, you can find the transformer, and if there is a fuse in the circuit.
    esquire1's Avatar
    esquire1 Posts: 2,483, Reputation: 209
    Ultra Member
     
    #8

    Oct 1, 2006, 06:47 AM
    tkrussell is right, it must be a control transformer. I was "***"uming that my answer was a given. Thanks for clarifing this tk
    mltascp's Avatar
    mltascp Posts: 6, Reputation: 1
    New Member
     
    #9

    Oct 1, 2006, 06:54 AM
    I think I found the transformer in my garage attached to the back wall. I removed it (after turning off the power). The left terminal is "10 VA" and the right terminal is "16V". The back of it says "Class 2 60 HZ" Line 120. Two black wires coming out the back.

    I have a new (less than one year old) air handler outside the house. Looked again and could not find a fuse.
    esquire1's Avatar
    esquire1 Posts: 2,483, Reputation: 209
    Ultra Member
     
    #10

    Oct 1, 2006, 07:00 AM
    The air handler is the unit inside,the condensing unit is outdoors. What model and make? To test transformer, with 120 volts coming into unit is there 24 volts coming out? If you are not comfortable working with electric call a serviceman. You must respect electric and work safely. The fuse will be on the inside unit if you have a cicuit board
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #11

    Oct 1, 2006, 07:12 AM
    Not all HVAC control systems have fuses. If the transformer is built-in on the HVAC unit, it usually has a fuse. If the transformer is added by the installer, such as yours being on the wall, there usually is no fuse.

    But you say the transformer is 16 volt? This may not be for the HVAC system, and may be for your door chime. Be sure this wiring connects to your HVAC system. And be sure your HVAC system can work with 16 v and does not need 24 v.
    mltascp's Avatar
    mltascp Posts: 6, Reputation: 1
    New Member
     
    #12

    Oct 1, 2006, 07:19 AM
    I believe I am very careful with electricity- I turn off the power going into the house before I disconnected this transformer. This transformer has two black house size wires putting out 120 V and two telephone size wires coming out (white and red) putting out 19 V ( I checked with my multimeter). Does that mean this transformer is OK? I did not see a circuit board in the air handler (inside the house) :) :) (neither did the condenser outside, by the way:D )
    mltascp's Avatar
    mltascp Posts: 6, Reputation: 1
    New Member
     
    #13

    Oct 1, 2006, 09:33 AM
    Hey guys... I found the problem.. it was the fuse inside the air handler (blown). It was hiding in plain sight and was staring right at my face. Anyway, I changed the 5 amp fuse and everything is working again, including the new Honeywell thermostat. Thanks for your perseverance in helping an electrically challenged guy:) . You guys probably saved me a few hundreds bucks by not calling in professional.

    Robert
    esquire1's Avatar
    esquire1 Posts: 2,483, Reputation: 209
    Ultra Member
     
    #14

    Oct 1, 2006, 09:47 AM
    Usually that is the problem. Glad you got it up and going

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Please Help!-thermostat wiring [ 1 Answers ]

I have 5 wires coming out of the wall: blue, yellow, red, white, and green. My thermostat only has 2 wires: red and black. How do I wire them to make my Central Air work?

HELP! Thermostat Wiring [ 3 Answers ]

We just bought an older house and are in the process of replacing 1960's wood paneling with drywall. The thermostat had been "painted" onto the paneling (many times over). After I removed the screws, I had to pry the t'stat away from the wall, which caused the wires to become dislodged from their...

Wiring a new thermostat [ 1 Answers ]

How do I wire a White-Rogers thermostat (Model#1F82-261) to a Goodman Heat Pump (Model#CPKE30-18). I know red wire goes goes to "R" terminal, green wire goes to "G" teminal but I need to know about the white, the yellow, the light blue, and the brown wire. My heat pump is a single stage cooling and...

Thermostat wiring [ 2 Answers ]

Is there a special thermostat for an electric furnace with A/C/. Don't you Want the blower to come on as soon as the electric heat is energized? In other words the same time.

Thermostat wiring [ 3 Answers ]

Hi all, great site! My problem is that we only have 3 wires coming up to our thermostat. We are installing central air and I was wondering if it is possible to wire the thermostat with only 3 wires?? Thanks :D


View more questions Search