    A/C Won't Start but Furnace Working
    Trane Split System 2TTR3036A1000A, 2 yrs old

    Hi.

    The furnace works fine. But when set to cool, neither the air handler or the compressor operate. Also, the "fan only" setting does not run the fan.

    I checked the 2 A slow-blow fuse on the board, and it's fine, but I assume that the furnace wouldn't operate if that was blown, anyway.

    On the T-stat, I shorted Y to Rc, but no response.

    The only thing I can think of is to check continuity between the T-stat and the furnace. Any other ideas?

    Thanks.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #2

    Apr 24, 2009, 04:40 PM

    Check to see if you have 24 volts between c and y at your control board with the t-stat calling for cooling.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #3

    Apr 24, 2009, 04:41 PM
    If so then check to see if ou have 24 volts outside at the ac unit
    DangNotAgain's Avatar
    DangNotAgain Posts: 3, Reputation: 1
    New Member
     
    #4

    Apr 25, 2009, 09:52 AM
    Thanks for the help.

    There is no voltage at all between Y and C (to clarify for others, this would be AC voltage).
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #5

    Apr 25, 2009, 10:21 AM

    If you have no volts between y and c at the control board then the t-sta must be bad. Take it off the wall and jump between y and r and see if the ac runs
    DangNotAgain's Avatar
    DangNotAgain Posts: 3, Reputation: 1
    New Member
     
    #6

    Apr 25, 2009, 10:49 AM
    I had previously jumped Y and Rc, according to the t-stat troubleshoot sequence, but nothing happened. I re-read the guide, and it says that for a 4-wire system (like mine), R and Rc should be jumpered. It's not jumpered. So, I jumped them, and the A/C started.

    That's strange, because it worked last season. I don't see how a jumper (and screw) for Rc could have gone missing over the winter. I never removed the T-stat, and there's no evidence of a screw or jumper wire. So, I don't know if the jumper was ever there. Anyway, under the assumption that it was, I guess I'll go get a proper fitting screw and put in a jumper.

    Correct action?
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #7

    Apr 25, 2009, 11:21 AM

    Yep sounds like you have it figured out. Very odd though indeed

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Furnace burner keeps working even if the blower is not working [ 3 Answers ]

My gas furnace (Trane XL80) this morning started to smell like plastic was burning from the registers, I went to check the furnace and noticed that the blower wasn't working so I turned the breaker off. My question is, should the burner had to turned off if the blower wasn't working for some time?

Furnace ignites but blower won't start till furnace shuts down. [ 7 Answers ]

(Nordyne/Miller G3RA)-I have a furnace HSI(glow plug) that will ignite and burn until it gets too hot and shuts down. As soon as the furnace shuts down the blower starts to circulate air. The blower circulating air cools the furnace and it reignites.Shortly after the furnace ignites the blower...

Furnace is not working [ 2 Answers ]

I have a thermostat that is showing the house to be 60 degrees while it is set for 72. The furnace will not come on when in the auto mode and when switched to on for the blower, Nothing will come on. This is a lennox elite system with a honeywell digital thermostat. Thanks for any help you can...

H4-H1 - when can you start working? [ 1 Answers ]

Hi - I am currently on a H4 visa and I have an employer who is willing to file an H1B visa for me ? When can I start working ? My H4 visa is currently valid until Sept 2009. Will this be a "change in status" and does it mean that I can start working as soon as I get the approval from the USCIS?

Start Up not working [ 4 Answers ]

Hi everyone... thanks in advance for any tip or help.. my CPU is flashing yellow on the start up button.. I have disconnected yet nothing is working... any advice?? Thanks... :)


View more questions Search