    Voltage variation in unbalanced three phase loads.
    Too long since I studied this in school, so I need some help. I do sound and for regional concerts/corporate events. We normally tie in to house power or a generator with 4o or 2o cable with cam lock connectors. Very common in our industry. These feed a three phase power distro (Motion Labs) which feeds racks and other equipment through L14-6 and Edison 20A connections.

    In one of the venues we work locally I have had severe problems with supply voltage variations when the load was unbalanced. The last situation was a relatively small PA and we also fed power to the Video guys. Current draws were on the order of 28A-17A-9A for the three phases. One of the phases was down to around 100V.

    The in-house people said that it was not their system, and the variation was because of the unbalanced load. We shut everything off and shuffled power around and achieved a load that was very close to balanced (can't ever be because the draw from the PA is always varying).

    My position is that a 200A service should not sag that much with only what I consider a small imbalance in load.

    Sorry about the long question, but I tried to lay out the whole situation. Thanks!
    sathe1963's Avatar
    sathe1963 Posts: 97, Reputation: 4
    Junior Member
     
    #2

    Apr 23, 2009, 06:39 AM
    Have u grounded neutral point (star point) of the generator? If no, try with this.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Difference between single phase and 3-phase motors [ 4 Answers ]

Difference between single phase and 3-phase motors

Can three single phase loads be driven individually by single three phase supply [ 2 Answers ]

Hi... I am new this community... You are doing great job of knowledge transfer... My question: Can three single phase loads be driven individually by single three phase supply? Please clear my doubt... :confused:

How do you usually connect three single phase loads to a three phase generator? [ 2 Answers ]

How do you usually connect three single phase loads to a three phase electric generator?:)

How to go from 200Amps/208V/3 phase to 600Amps/480V/3 phase [ 2 Answers ]

I am starting a business and have equipment that requires 600Amps/480V/3 phase, but the site I want to rent has only 200Amps/208V/3 phase. Is there anything I can do to get the required power on that site? Any equipment I can buy to achieve this goal? I understand it may be costly. Thank you.

How am I going to size my 3 phase X'mer with 1 phase load using current as reference [ 3 Answers ]

Hi, I'm Peping: I have 90 pieces of single phase loads with current of 2 Amperes. This will be loaded to a 3 phase transformer, Wye connected having a line to line voltage of 220 Volts. What will be the size of the transformer required for the mentioned loads? Many thanks, Peping


View more questions Search