    BX to Romex?
    I have an older home with the metal sheilded 2 conductor cable. 2 20 amp lines were added to the kitchen, but still using the metal sheilded 2 conductor cable. Is it OK to connect this in a box to romex? [grounding the ground to the sheild] The kitchen is being updated again. I am very handy (ex automechanic) and will add one GFI protected outlet every 24 inches of counter.
    ohb0b's Avatar
    ohb0b Posts: 215, Reputation: 14
    Full Member
     
    #2

    Apr 19, 2009, 07:40 PM
    Check your local codes... there may be a reason they used "BX" (Almost no one calls it that anymore, you must be an old guy!) instead of Romex.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #3

    Apr 19, 2009, 08:04 PM
    Ohbob... methinks you must be a young guy... and have no idea what BX is... right?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #4

    Apr 19, 2009, 08:08 PM

    FWIW:
    What is Romex/NM/NMD? What is BX? When should I use each?
    ohb0b's Avatar
    ohb0b Posts: 215, Reputation: 14
    Full Member
     
    #5

    Apr 19, 2009, 10:41 PM
    Wish I was a young guy!

    Type NM (Non-Metallic Sheathed) cable is commonly called "Romex." Which I believe is a trademark of the Rome Cable Company. In Canada, there is a similar product called "Lumex."

    As for "BX" the NEC calls it Type AC (Armor Clad) or Type MC (Metal Clad) They both have a spiral wrap armor. The chief difference between the two types is the insulation of the underlying wires. There is also a smooth sheath MC cable, which is not commonly used.

    I can't verify this, but here is the story I heard: There once was a Greenfield company, who manufactured flexible conduit. (Metallic Flexible Conduit is still referred to as "Greenfield" in the trade.

    The story goes, they used to rope houses with flexible conduit, then fish wires through it. Someone at Greenfield developed a conduit with wires already installed... it was their "B" product line, and it was eXperimental. I can't verify this tale, but it sounds too good to be true.

    Type NM (Romex) is used mainly in residential construction. Some areas of the country, the local code specifies armor clad cable, usually for protection against rodents.

    If Romex is approved for your location, you may continue the existing "BX" run in Romex, as long as you make the termination inside an approved box. (NEC 320.40)
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #6

    Apr 20, 2009, 04:30 AM
    BX must be more of a locational thing. Very few around here use the term AC. It's either BX or MC.

    You have to remember, if the AC does not have the thing bonding strip the sheathing CANNOT be used as the equipment ground.
    250.118(8)
    320.100
    Dpfiling's Avatar
    Dpfiling Posts: 18, Reputation: 2
    New Member
     
    #7

    Apr 22, 2009, 02:55 AM

    Stanfortyman is correct. The wound armored sheath is not permitted to be used as a grounding conductor. You must have a separate ground wire all the way back to the panel.
    WKL3's Avatar
    WKL3 Posts: 2, Reputation: 1
    New Member
     
    #8

    Apr 26, 2009, 03:45 PM
    Quote Originally Posted by Dpfiling View Post
    Stanfortyman is correct. The wound armored sheath is not permitted to be used as a grounding conductor. You must have a separate ground wire all the way back to the panel.
    Renovated Kitchen:

    Stanforyman & all. As I understand things from reading, the NEC was updated in 2008 which included 250.118(8) which states that the Flexable Metal Shield is no longer acceptable for a ground.

    Then, this requires a new NM 12 gauge Romex cable?? (one per circuit breaker) Sounds like I need to stop in the town office and talk to the inspector to learn the latest and greatest. The entire job will be inspected (I'm just running the electrical) and want no headaches.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #9

    Apr 26, 2009, 05:11 PM
    Quote Originally Posted by WKL3 View Post
    Stanforyman & all. As I understand things from reading, the NEC was updated in 2008 which included 250.118(8) which states that the Flexable Metal Shield is no longer acceptable for a ground.
    This is nothing new. It has been this way since "modern" AC cable (with the bonding strip) was introduced many years ago.
    lalo13187's Avatar
    lalo13187 Posts: 1, Reputation: 1
    New Member
     
    #10

    Oct 22, 2013, 07:12 AM
    What is the difference between romex and bx cable? I need answer asap please thanks
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #11

    Oct 22, 2013, 09:12 AM
    The fastest answer can be found on the internet...
    You'll get pictures and everything and you won't have to wait...
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #12

    Oct 22, 2013, 10:24 AM
    "NM" ("Romex", is a brand name) for a non-metal sheathed cable. AC ("BX" is Slang for Bronx, NYC where it was made originally) is a metal shielded cable.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #13

    Oct 22, 2013, 02:03 PM
    Quote Originally Posted by lalo13187 View Post
    What is the difference between romex and bx cable? I need answer asap please thanks
    Read the previous posts.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Allowable # of romex in a 2" romex connector [ 2 Answers ]

Hi, I would like to know the maxamum allowable romex wires can be secured in a 2" romex connector. Thanks

Romex to spa box [ 7 Answers ]

I am mounting a spa box on a new exterior wall. I have 6-3 +gnd romex wire running from the panel to the box. I want to bring the wire from inside the wall right into the back of the spa box. Is this okay? I have noticed some spa boxes have knock-outs on the back while others do not. If I do...

15A vs. 20A on #12 Romex [ 10 Answers ]

We are running #12 Romex wire for circuits from the panel. I want some of the breakers in the panel to be 15amp and some to be 20amp. My electrician says that they should all be 20amo because #12 Romex is code for 20 amps. I said sure but it shouldn't matter is we go smaller than code (i.e....

Romex or bx [ 1 Answers ]

Hello, My niece is having some electrical work done in her hi rise condo, in manhattan NYC I notice romex cable being used, I always thought bx cable was code for NYC Any info is appr. Thank you

Bx or romex 240 or 120 [ 5 Answers ]

Replacing old bathroom fixtures in a 100 yr old house. Has old 2 wire bx and I want it on its own circuit. The supply comes in from another room to the ceiling box where it goes to another room and to the wall switch then from there it goes to the medicine cabinet. I want to have this room on its...


View more questions Search