    20amp circuit in 3 wire kitchen split
    I recently bought a house & I'm renovating the kitchen.

    I have 2 duplex receptacles within 1.5m of the sink. I need to make both of these outlets GFCI protected but they are both 3 wire kitchen splits. GFCI outlets do not exist for 3 wire split circuits.

    I have a 25 year old Commander BC 32125 panel and I can't get 2 pole 15amp GFCI breakers for this panel to replace the standard 2 pole breakers on these two circuits.

    Could I put a single pole 20 amp breaker in the panel and run the two 14 gauge hot wires in parallel to a new GFCI 20amp t-slot outlet (for each outlet)? 2-14 gauge wires should be better than a single 12 gauge to handle the 20 amp circuit right?

    But then there is the whole electrical code thing...

    I may be faced with replacing the panel or trying to pull new 12 gauge wire (which is virtually impossible)

    Thanks to any and all who reply!
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Mar 30, 2009, 01:44 PM
    25 years is not that old. Are you sure it is not made? Did you try a real electrical supply house?

    You could also install a small sub-panel and move that circuit to the sub-panels and use a 2p GFI breaker in that.
    brekkster's Avatar
    brekkster Posts: 3, Reputation: 1
    New Member
     
    #3

    Mar 30, 2009, 02:25 PM
    I'm not sure what the split is for
    But if the split is just to have 2 circuits at each kitchen receptacle what you could do is locate where the circuit starts and where it ends "making sure its not feeding anything else in the house" if it is just the kitchen receptacles use only 1 of the feeds on the line side and the load side and cap off the unused feed and load wires
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Mar 30, 2009, 03:04 PM
    Split receptacles in kitchens used to be a Canadian code thing.
    ohb0b's Avatar
    ohb0b Posts: 215, Reputation: 14
    Full Member
     
    #5

    Apr 13, 2009, 02:12 AM

    "Split" circuit? I think you are referring to a "multiwire" brasnch circuit. The reason you can't find a two-pole GFCI breaker is there is no such thing for this application.

    GFCI's work by comparing the current in the hot and neutral wires, and tripping if there is any imbalance. On a multiwire branch circuit, the neutral wire carries the current imbalance.

    The good news is the GFCI compares the current on the hot and neutral wires going TO THE RECEPTACLE. So, if you pigtail the GFCI's into the circuit instead of landing the wires directly on the terminals, they will see a balanced current in both wires.

    Landing the two 14 AWG wires on the same breaker would make them both the same phase, but the wire is not really parallel, (one would go to half the receptacles, the other would go to the other half) so you will not have any more cross sectional area. As a side note, the NEC does not allow paralleling wires under 1/0.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #6

    Apr 13, 2009, 04:50 AM
    Two -pole GFI breakers ARE available for situations just like this, but maybe not that fit the OP's panel.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #7

    Apr 13, 2009, 02:34 PM

    ..
    Attached Images
     

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Need a 20Amp Circuit but no room in the panel [ 21 Answers ]

Hi, I need to run a dedicated 20AMP circuit for my over the range microwave but have a problem. There is no room in the box to add another breaker. On top of it, all of the single pole breaker are already doubled up. Can anyone help me figure out how to squeeze one more run in here? ...

How many recessed 65 W lights on one 20amp circuit? [ 5 Answers ]

My question is pretty straight forward. I am going to have 20 recepticals and 16 recessed lights to wire. I have plenty of room for additional breakers in my box I also prefer using 20 amp breakers 12/2 wiring. How do you calculate how many lights and recepticals can go on one circuit? My maximum...

How many light on one circuit? 15-20amp? [ 1 Answers ]

HI;:) I am remodeling my kitchen and installing new lights. I will be installing 8 Halo resesed 6" cans with 60w bulbs but they are rated for 75w, and 2-2tube floresent light fixtures, and they all will be split up between 4 switches but might be all on at the same time. There is one existing...

20amp circuit breaker, 15 amp receptacles [ 2 Answers ]

I have a 20amp circuit breaker with 15 amp receptacles and light switches on #12 wire with a load of 1700, is this allowable? If not, and I change to a 15 amp circuit breaker, is the 1440 watt safety load in the code or is it a non-code safety suggestion?

Outside GFI circuit - 15amp outlet on 20amp circuit [ 1 Answers ]

I need a better understanding of what I should do when setting up my new outdoor circuit. I've got a circuit that runs about 150 feet, so I'm installing 10g wire to allow for the voltage drop. I read in the Home Depot Electrical 123 book that I can have at most a 15amp circuit with 10g wire on...


View more questions Search