Apr 6, 2009, 11:24 AM
|
|
Wire Size?
I have 200 amp service coming into my home. I want to wire my shop which is 130 ft from my panel box. Going to have about 20 120volt outlets, 20 lights. Also will have air compressor, and maybe a welder, so I'll need 240 as well I guess. What size wire would I need to do this? Also, would expect to have 100 amp subpanel, I guess.
Thanks
|
|
 |
New Member
|
|
Apr 8, 2009, 04:26 PM
|
|
I have decided to go with 6/3 with ground. I believe this should be sufficient. Thoughts?
|
|
 |
Electrical & Lighting Expert
|
|
Apr 8, 2009, 05:34 PM
|
|
#6cu at that distance will give you about 50 amps max before voltage drop is a concern.
This should be fine unless the welder you are considering is a typical stick welder.
|
|
 |
Ultra Member
|
|
Apr 8, 2009, 08:07 PM
|
|
#6 to a 100 amp sub panel?. NO CAN DO..
|
|
 |
Electrical & Lighting Expert
|
|
Apr 9, 2009, 06:17 AM
|
|
 Originally Posted by Missouri Bound
#6 to a 100 amp sub panel???....NO CAN DO..
What does the size of the panel matter? When was the last time you saw a 12, 16, 20, etc, space panel rated less than 100A?
As long as the feeder breaker is proper #6 is perfectly fine, and very commonly used as a sub-feeder.
|
|
 |
Electrical & Lighting Expert
|
|
Apr 9, 2009, 06:19 AM
|
|
For a FULL 100A (80A continuous) feeder you'd need #4cu or #3cu in this case.
|
|
 |
New Member
|
|
Apr 9, 2009, 08:31 AM
|
|
Yeah, I realize #6 is 60 amp, but I thought I could still use a 100 amp panel box. Do you guys think I would be better to go with #4? Thanks for your imput.
|
|
 |
Electrical & Lighting Expert
|
|
Apr 9, 2009, 08:50 AM
|
|
You CAN use a 100A panel. If you go with#4 you can use a 70 or 80A breaker.
|
|
 |
New Member
|
|
Apr 9, 2009, 10:24 AM
|
|
2/3 wire is rated up to 95 amps.do you no the nec codes for your area. Some require a circuit breaker if your running 6 circuits or more from your sub-panel
|
|
 |
Ultra Member
|
|
Apr 9, 2009, 07:12 PM
|
|
I assumed ( out of U and ME) that you intended to use a 100 amp breaker in this 100 amp panel. But whatever main you use will dictate the size of the wire, as Stan eluded to. :)
|
|
 |
Uber Member
|
|
Apr 9, 2009, 07:20 PM
|
|
The main doesn't dictate the size of the panel, the feeder breaker does. The main in the sub could be 100 A with a 60 Amp feed breaker. In this case the 100 A breaker is just a disconnect.
Reminder: 130' sounds like the shop is in a detached structure. If it is a ground rod is required.
|
|
 |
New Member
|
|
Apr 9, 2009, 07:30 PM
|
|
Yeah, it is detached, and there is already a ground rod in place. I bought the place and they had service out there, but it was overhead, and when it went into the shop, they had 3 of the outdoor style shutoffs with the fuses. I don't like it, and want to modernize. It was built in 67, and they just kept adding on as they needed. Thanks for all your guys' help.
|
|
 |
Printers & Electronics Expert
|
|
Apr 10, 2009, 07:00 AM
|
|
Brotzmr,
Could you please explain this quote for me?
"2/3 wire is rated up to 95 amps.do you no (know?) the nec codes for your area. some require a circuit breaker if your running 6 circuits or more from your sub-panel"
You have to have a breaker to protect the feeder circuit from the panel. At the subpanel, you cannot have more than six switches (breakers). However, you can have a master cut off switch or a main breaker to cut the power in an emergency.
NEC is National or International set of electrical codes, not local. Local governments may have codes that change or modify the NEC codes.
What kind of 2/3 wire are you talking about? What insulation do you think should be on the wire? Have you looked at the NEC and noticed that #4 AWG is used for 100 amp feeder circuits?
|
|
 |
Ultra Member
|
|
Apr 10, 2009, 05:18 PM
|
|
Lets get past the semantics... JHESSSE... is it your plan to have a 100 amp service in this shop? I based my comments on that, and just wondering if that is indeed the case, or I speculated wrongly. With the lighting and outlet load you want, and the compressor and welder usage you probably don't need a 100 amp service, unless the shop will be used by a few people at a time and the equipment will be operated simultaneously. Only you know that.
|
|
 |
New Member
|
|
Apr 13, 2009, 10:15 AM
|
|
No, not necessarily 100 amp. Was just going to get a panel rated for 100 amps. Sorry for the confusion.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Wire size & conduit size for 60 am subpanel 150 from source
[ 9 Answers ]
Indiana question:
I want to install a 60amp subpanel 150 feet from the main panel. This is all exposed runs both inside and out in a commercial envirenement.
What gauge and type of copper wire and what size conduit whould I use. How often should insert a junction box in the run.
John
Sub Panel AMP Size and Supply Wire Size
[ 1 Answers ]
I would like to install a sub panel in my garage I was told to run 6/3 Romex to supply the sub panel and have done so. The run is about 65 feet and I am now wondering after reading this site what is the max I can get for this size wire? I plan to supply a compressor (20 amp) and the garden...
Vintage stove- 3 wire 220v, what size wire?
[ 1 Answers ]
We recently purchased a vintage Crosley range. The old wire was a 3-wire 220v, connected to terminals in the back- the black and red wires were actually 6 or so copper strands, and the white was a silver metal. My question is, what amperage do you think I need? Will 10 be enough?
Thanks for your...
Wire Size and panel size
[ 6 Answers ]
I have a separate small living quarters that is a single room that is about 180 feet away from the main panel. It is going to get another little bed room a small kitchen and a bathroom also maybe a washer. The main panel is a 100 amp meter socket combo. What should I upsize the main panel to? ...
4 wire home service entrance wire size
[ 1 Answers ]
Mobile home requires 4 wire electrical service entrance wire. Distance is 160 foot from meter to breaker panel. 220V service. What size wire do I use? Can I use diff. size for neutral and ground?
View more questions
Search
|