Ask Experts Questions for FREE Help !
Ask
    frissbeegolfer's Avatar
    frissbeegolfer Posts: 16, Reputation: 1
    New Member
     
    #1

    Mar 4, 2009, 11:09 AM
    Gibson furnace cycling 2,3,4 times before starting
    Hi, I have a gibson m#KG6RK 072C-12A s#KGA021204267.natural gas.I've cleaned the flame sensor,that seem to work for a day with the furnace starting up on the first try.then I inspected further and found some wires that melted on the inducer\flu parts.so I cut out the bad part of the wire and reconnected them ,that seem to work for about a day.I did find a ground wire screwed to the inside of the furnace that wasn't hooked up to anything and it doesn't look like it was ever hooked up to anything.then I check to see if it had a good ground and the copper wire from the fuse box was grounding the switch box that connects to the furnace,so I'm assuming that the steel casing from the switch is grounding it properly.so sometimes the furnace tries five times to start and it doesn't,which gives me five flashing lights ,meaning (check ground).now when the furnace attemps to start I hear the inducer making a weird noise.I can't explain the noise other than it sounds like its vibrating.do you think my flame sensor is bad is there a way to check the resistance with a analog testing meter.I hope I left enough info any help will be greatly appreciated.thanks,greg
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #2

    Mar 4, 2009, 04:09 PM
    The ground referred to in the service legend is likely the ground path between the burner area and the circuit board/ignition module. Flame sensors rarely fail, but will certainly oxidize and require periodic cleaning - once every fall is usually adequate. If the circuit board/ignition module has metallic standoffs for mounting, they may be providing the ground. If this is the case with yours, make sure the screws are securely fastened.
    frissbeegolfer's Avatar
    frissbeegolfer Posts: 16, Reputation: 1
    New Member
     
    #3

    Mar 5, 2009, 03:03 PM
    Thanks for the reply.the circuit board/ign mod is connected to the furnace by plastic fastners.I have a red(hot) wire and a white (nue) wire coming in to the furnace but no ground wire I don't know how the board is getting a ground.other than maybe from the humidifier low voltage( converter?) which is tied to the gas pipe(grounded).then plugs in to the" hum" nue and "hum" hot on the board if that makes any sense.my light is now flashing 4 times meaning ign failure\bad ground.I would upload pics but can't seem to them on my PC right now.thanks for your help. p.s.s I hope I'm replying to you correctly
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #4

    Mar 5, 2009, 06:40 PM
    Quote Originally Posted by frissbeegolfer View Post
    My light is now flashing 4 times meaning ign failure\bad ground.
    I don't think this has anything to do with the unit being grounded or ungrounded. The ignition module/circuit board must be grounded to the unit. If the ground connection is compromised, weak flame current will lead to ignition lockout. Check near the burner area for a ground wire leading to the module/board. Inspect for damage and/or poor connection.
    frissbeegolfer's Avatar
    frissbeegolfer Posts: 16, Reputation: 1
    New Member
     
    #5

    Mar 7, 2009, 12:57 PM

    Hi,there is a ground wire going to the ignition module.where should I go from here? Thanks,greg
    frissbeegolfer's Avatar
    frissbeegolfer Posts: 16, Reputation: 1
    New Member
     
    #6

    Mar 7, 2009, 01:35 PM

    The igniter had a resistance of 100 ohms,the roll out switches were 0 ohms, so I think there is nothing wrong there.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Gibson Furnace [ 9 Answers ]

Gibson Furnace will blow cold air sometimes instead of warm air. I believe it to be a problem with a wire because we had it worked on before. There are also two lights - one stays on continuously and the other one will blink. Is this something I can repair myself? If so, how? The furnace is...

Gibson furnace cycles different all the time [ 15 Answers ]

Hi,I noticed my gibson furnace m#KG6RK 072C-12A S#KGA021204267 cycling an not starting. It locked out.got a flashing light said I had a bad ground.so I took it apart and found nuetral wire melted to flue and other wires melted to inducer.I clip out bad wires and reconnected and cleaned off flame...

Pressure switch stuck open gibson furnace [ 3 Answers ]

I have a gibson forced hot air furnace and a have a code that is telling me that the pressure switch is open. If I drain the water out of it it will run for a short period.. Do you think I need a new pressure switch or do I have a drainage line clogged. Model number KG6R060C-12a

Furnace cycling [ 1 Answers ]

I have a Trane gas furnace w/no standing pilot it's electronic. Anyway when the t-stat calls for heat it will fire up and the shut of within 5 secs. It will do this approx. 4 times before it will eventually lock itself out and the blower will continue to run not ever reaching setpoint. I know...

96 Accord Problem starting some times [ 3 Answers ]

I currently have a 96 honda accord. It is a 4 cylinder engine and is standard transmission. My car sometimes will start on first try, but most of the time it takes at least 3 or up to 8 times before it starts. It always cranks and all the lights come on, so I am not sure what might be wrong. I...


View more questions Search