Small appliance with 20 amp rating
I am finishing my basement which will include a bar. I would like to place a small 2 burner built-in cooktop rated at 20 amp (110 v). Do I need to place this on a dedicated circuit? Can I place this on my soon to be shop circuit which will be 20 amp breaker 12-2 wire with about 4 outlets only? ( I am sure the shop outlets will not be in use when the cooktop is)
|
|
 |
Home Repair & Remodeling Expert
|
|
Mar 6, 2009, 11:34 AM
|
|
I'd recommend a dedicated circuit for the cooktop since it's rated at 20 amps. Anything else on the circuit will cause and overload. I know you said the other outlets would not be used while the cooktop is in use but this is not a 100% guarantee down the road.
|
|
 |
New Member
|
|
Mar 6, 2009, 11:50 AM
|
|
OK, this may cause a problem. I have a 100 amp main with 20 slot GE box, all full. I have read I can have max 48 breakers? So I am planning on already pulling 2 of the 20 amp and replacing them with 4 GE 1/2" breakers and then doing the same with 2 of the 15 amp breakers. so will pulling another 20 amp for cooktop circuit be a problem? this will leave me 1 open 1/2" slot for total of 26 breakers.
|
|
 |
Home Repair & Remodeling Expert
|
|
Mar 6, 2009, 11:55 AM
|
|
Are you saying that you will be using one of these 1/2 sized breakers for the cooktop or are you doing that switch out for some other reason?
|
|
 |
Uber Member
|
|
Mar 6, 2009, 11:59 AM
|
|
This somewhat depends on how you count. There isn't a breaker limit, but rather a pole limit. e.g. a 240 volt breaker has two poles, so it counts as 2. That number should not be exceeded.
You can add a small sub-panel, say 60A if you needed too.
|
|
 |
New Member
|
|
Mar 6, 2009, 12:07 PM
|
|
I would need to free up a slot somehow, but I would probably try to find a circuit that can be placed on a 1/2" rather than a dedicated one
|
|
 |
New Member
|
|
Mar 6, 2009, 12:10 PM
|
|
Kiss, would the subpanel be preferred over the 10 1/2" breakers?
|
|
 |
Home Repair & Remodeling Expert
|
|
Mar 6, 2009, 12:27 PM
|
|
The half sized breakers are safe, UL approved and cheaper/easier than a sub.
|
|
 |
Electrical & Lighting Expert
|
|
Mar 6, 2009, 12:28 PM
|
|
The panel will only accept skinny breaker if it is designed to. You can't simply put them in anywhere.
If it is a 100A panel it is most likely that you cannot out hem in at all, and if you can probably only in the bottom 4 spaces.
The 42 pole limit is over all. Not in every panel.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Spraying appliance
[ 1 Answers ]
Can you have a stove top and oven door sprayed another color?
Appliance installation
[ 5 Answers ]
We are trying to remove our old over the range microwave to replace it. We can't find any screw or clicks even holding it in place. How do we get it down?
Electrical outlet rating vs. Circuit breaker amperage rating
[ 5 Answers ]
Hello to all,
I am new to this forum, please excuse me if this question has been answered.
I just bought a Thermal Dynamics Plasma cutter. It has a Nema 50-P plug end on it, which I assume is to be plugged into a Nema 50-R outlet.
In looking in my reference book, this is a 3 wire...
View more questions
Search
|