    Size of wire required for 70 amp boxservice
    I am installing a 70 amp outdoor box, one 30 amp 220v and two 20 amp 110v breakers for a travel trailer. The meter loop is rated at 125 amp. I am running this service from the meter loop, main box under ground to the 70amp outdoor box. WHAT SIZE WIRE WILL I NEED TO USE, the total run from end to end is 120'.
    Thanks in advance for your assistance.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Mar 4, 2009, 05:08 AM
    Is there a disconnect or panel at the meter. You CANNOT simply come out of an existing meter.

    You would need #6cu or #4al conductors in conduit. If you run cable then #4cu or #3al.
    Jamdozer57's Avatar
    Jamdozer57 Posts: 2, Reputation: 1
    New Member
     
    #3

    Mar 5, 2009, 01:39 PM
    Quote Originally Posted by stanfortyman View Post
    Is there a disconnect or panel at the meter. You CANNOT simply come out of an existing meter.

    You would need #6cu or #4al conductors in conduit. If you run cable then #4cu or #3al.
    Thanks for the response;
    There is a breaker panel under the meter can with multiple blanks for the breakers.

    What breaker would be required for this application and would I have to be concerned about a voltage drop over for this length of run?
    badmom66's Avatar
    badmom66 Posts: 3, Reputation: 1
    New Member
     
    #4

    Mar 11, 2009, 06:55 AM

    The distancce from meter is 200 ft

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire size & conduit size for 60 am subpanel 150 from source [ 9 Answers ]

Indiana question: I want to install a 60amp subpanel 150 feet from the main panel. This is all exposed runs both inside and out in a commercial envirenement. What gauge and type of copper wire and what size conduit whould I use. How often should insert a junction box in the run. John

Sub Panel AMP Size and Supply Wire Size [ 1 Answers ]

I would like to install a sub panel in my garage I was told to run 6/3 Romex to supply the sub panel and have done so. The run is about 65 feet and I am now wondering after reading this site what is the max I can get for this size wire? I plan to supply a compressor (20 amp) and the garden...

Cable size required [ 2 Answers ]

I have a house 60m from a transformer 240v single phase 50hz, and a shed which is 220m from the transformer. I want to run under ground power to both from the transformer. Is 220m to far to run this power to the shed, If not what size/type of cable do I require. The shed is not a workshop rather it...

Vintage stove- 3 wire 220v, what size wire? [ 1 Answers ]

We recently purchased a vintage Crosley range. The old wire was a 3-wire 220v, connected to terminals in the back- the black and red wires were actually 6 or so copper strands, and the white was a silver metal. My question is, what amperage do you think I need? Will 10 be enough? Thanks for your...

4 wire home service entrance wire size [ 1 Answers ]

Mobile home requires 4 wire electrical service entrance wire. Distance is 160 foot from meter to breaker panel. 220V service. What size wire do I use? Can I use diff. size for neutral and ground?


View more questions Search