    Grounding 10/2 wire
    I noticed the other day that the 10/2 wire going from my breaker box to the well pump was not grounded. The ground wire at both ends of the cable was cut off... only the black/white wires were connected. I have 2 questions:
    Should a 20amp double pole breaker be connected to #10 or #12 wire?
    Is their any reason why the ground wire should be cut off the #10 cable at both ends?
    Thank you,
    Savroman
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Feb 26, 2009, 06:52 AM

    A 20 Amp breaker can be used with #10 or #12. The #10 may have been used for Voltage Drop, but motor only needed 20 Amp Protection.
    Ground needs to be hooked up at both ends. Turn Breaker off to Minimize chance for a shock when hooking up ground.
    savroman's Avatar
    savroman Posts: 2, Reputation: 1
    New Member
     
    #3

    Feb 26, 2009, 07:19 AM
    Thank you for your answer... should I replace the whole 10/2 cable or buy a #10 ground wire and run it separately?
    Savroman
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #4

    Feb 26, 2009, 07:24 AM

    I would pigtail at the panel if possible, and at the pump, maybe have it go to a disconnect, then pump, may keep you from replacing wire.
    A separate # 10 is not acceptable protection for the 2 hot wires.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Grounding a fixture to wire w/ no ground [ 1 Answers ]

Hello. I am replacing a bathroom light/exhaust fan. The previous llight had no ground wire and the wire leading to the unit has no ground. The new unit does. How do I ground the unit? Thanks for your time E

Grounding wire pigtail [ 1 Answers ]

I just changed an exterior light on my older home. I connected the house grounding wire with the light grounding wire. But, the directions mentioned a pigtail grounding wire (not included of course) and there is a green grounding screw on the metal plate. So do I need to get/install a grounding...

Two-wire conduit grounding [ 1 Answers ]

My new furnace has metal box with an electrical plug and switch on the side. Three-wire conduit (with black, white and green wires) runs from that box up to an overhead light with a metal box. An older piece of two-wire conduit (with black and white wires) runs from the light to the breaker box. ...

SPA disconnect switch grounding wire requirement [ 1 Answers ]

I'm installing a 240V/60A SPA approximately 85 feet from the house service panel. I'm going to run 3 individual #6 conductors (THN or better) from the service panel to the SPA GFI disconnect box via 1 inch PVC conduit. The SPA is about 7 feet from the disconnect box. The disconnect box instructions...

Hard wire 3 wire to 4 wire 220 service [ 1 Answers ]

How do I hard wire my 3 wire (red,blk & bare copper wires) 220vac cooktop to the 4 wire (black/white stripe,black/red stripe, blk/blk & bare alum wires) in the house supply j-box ?


View more questions Search