    Goodman Air Handler AH2429 heat won't shut-off
    I have a Goodman Air Handler AH2429 and the heating furnace won't shut-off.

    When I disconnect the red wire from the furnace leading to the thermostat the furnace shuts-off and when I reconnected the wire, the furnace heat turns on (runs). I also checked the thermostat wiring - red to Rh, yellow to yellow, blue to blue and white to white. I have a honeywell RTH230B thermostat.

    I guess that I have a faulty time relay? Am I right?

    Please help me... my sincerest thanks...
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Feb 16, 2009, 11:05 AM
    When I disconnect the red wire from the furnace leading to the thermostat the furnace shuts-off and when I reconnected the wire, the furnace heat turns on (runs).

    You are doing what the thermostat should be doing.

    It could be

    Low voltage wiring shorted between the furnace and thermostat.

    Defective thermostat causing a call for heat all the time.
    nquijote's Avatar
    nquijote Posts: 2, Reputation: 1
    New Member
     
    #3

    Feb 16, 2009, 01:57 PM
    Quote Originally Posted by hvac1000 View Post
    When I disconnect the red wire from the furnace leading to the thermostat the furnace shuts-off and when I reconnected the wire, the furnace heat turns on (runs).

    You are doing what the thermostat should be doing.

    It could be

    Low voltage wiring shorted between the furnace and thermostat.

    Defective thermostat causing a call for heat all the time.
    HVAC1000,

    Does your answer has two probabilities: one is I have a faulty time relay and the other, my thermostat is defective? Please answer back...
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Feb 16, 2009, 03:08 PM
    Here are the two answers.

    (1)Low voltage wiring shorted between the furnace and thermostat.

    (2)Defective thermostat causing a call for heat all the time.

    These answers were based upon your action taken with the connect and disconnect of the red wire at the furnace. I have no idea where you got a defective time delay from?

    If the thermostat is not calling for heat and you connect and disconnect the red thermostat wire you are acting like a substitute thermostat working the furnace. This would lead one to believe that the problem is as I mentioned in number 1 or 2 above. It could be other items but I would check those first using normal diagnostic tools.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Goodman heat pump won't shut off [ 1 Answers ]

We have a Goodman heat pump. The furnace began to act up when we turned the heat to emergency heat (temps were getting in the teens). The emergency heat would not shut off and the temp in the house got to about 77 (thermostat set on 68). Finally, it shut off and we turned it back to regular heat....

Air Handler will not shut off? [ 2 Answers ]

My air hadler will not shut off. I disconected the thermo, and it still runs. Emergency heat light is not on but it blows warm air.

Wiring air handler goodman A-30 [ 2 Answers ]

Trying to take goodman air handler A-30 from straight ac and convert to heat pump fan coil only has three low voltage wires how do I go about wiring?

Carrier Air Handler - Blower Won't Shut Off [ 3 Answers ]

I have a Carrier heat pump package unit with a Carrier air handler, both from late 70's/early 80's (Model number illegible on sticker). When the weather was cold a couple of months ago, the blower would run constantly, making the house unbearably hot. Turning down, turning off, or disconnecting the...

Wiring Diagram for a Goodman Air Handler [ 4 Answers ]

Does anyone know where I can obtain a wiring diagram/schematic for a Goodman Air Handler? The Model# is AEPT 030-00C-1A; Serial #0508047623; 208/240v - single phase; 2 amp 1/2 HP motor. Thanks. Eugeno


View more questions Search