Feb 11, 2009, 05:27 PM
|
|
Wears Thermostats Wireing
I have Mears Thermostats in my home. They have (3) three wires on them
RED is load
BLACK is line
WHITE??
Thermostats tried a singel pole Thermostat with (2) wires RED & BLACK tieing off the White
I have tried a double pole using t1 for load (RED) and L1 for line (BLACK) and tie off l2 & t2 togather.
|
|
 |
Senior Member
|
|
Feb 11, 2009, 06:18 PM
|
|
Are these line voltage thermostats for electric strip heat? Or are they low voltage thermostats?
|
|
 |
New Member
|
|
Feb 12, 2009, 08:14 AM
|
|
This is for baseboard heat (220 volt) the wires are 12's
|
|
 |
Senior Member
|
|
Feb 14, 2009, 05:13 PM
|
|
Since this is 240 volt, both wires (black & white) coming from the power source are hot. Each wire going to the heat will connect (thru the tstat) to each of the load wires. If you use a double pole thermostat, connect each incoming power wire to the line terminals of the tstat, and each wire that goes to the heat to the load terminals on the tstat. If the tstat is single pole, just wire nut one of the line wires to one of the load wires and hook the other wires to the tstat as I described above. I prefer double pole line tstats because when they are off, the heat unit has NO voltage hooked to it.
|
|
 |
New Member
|
|
Feb 14, 2009, 08:02 PM
|
|
 Originally Posted by EPMiller
Since this is 240 volt, both wires (black & white) coming from the power source are hot. Each wire going to the heat will connect (thru the tstat) to each of the load wires. If you use a double pole thermostat, connect each incoming power wire to the line terminals of the tstat, and each wire that goes to the heat to the load terminals on the tstat. If the tstat is single pole, just wire nut one of the line wires to one of the load wires and hook the other wires to the tstat as I described above. I prefer double pole line tstats because when they are off, the heat unit has NO voltage hooked to it.
I have tried both of these ways and my heat iis still not working. What dose the WHITE wire do. I have been told that it is a common line but what function does it preform and how or where dose it fit in to the single or double pole thermostat. Thank you for your help so far it has been good to talk to someone that know what I am alking about .
|
|
 |
Senior Member
|
|
Feb 16, 2009, 12:27 PM
|
|
If you hooked the thermostat up the way I said, it would sound to me like your heat strip is dead. If you check the resistance between the two LOAD (heater) wires, you should get a reading somewhere in the range of 12 - 25 ohms (for 16 ft of heat) up to 115 ohms or a bit above (for 2 ft of heat). That is a range of readings that covers most installations. You should also verify the voltage on the two LINE wires. If that doesn't show something close to 240 volts, you could have a problem there. You could also do a current check and verify the wattage used, but that's a bit more technical. If you don't have the equipment or feel comfortable doing those measurements, call an electrician.
The white wire is actually another hot conductor in this situation. It carries the power from the opposite leg (referenced to the black conductor) of your electrical system. In this situation, it is NOT a common or neutral conductor. Technically it should be marked with tape or something to show it is a hot conductor.
|
|
 |
New Member
|
|
Feb 20, 2009, 12:39 PM
|
|
I have 22 ohms at this line. I know that the strip works because them old thermostat is bad it will not shut off or turn down. What will happen if I connect the white wires to a 2 polled thermostat
|
|
 |
Senior Member
|
|
Feb 20, 2009, 04:53 PM
|
|
Connect both black and white LINE wires to the LINE TERMINALS on the new double pole thermostat. Connect both LOAD (heater) wires to the LOAD TERMINALS on the new thermostat. It will work correctly.
|
|
 |
New Member
|
|
Mar 3, 2009, 02:47 PM
|
|
 Originally Posted by EPMiller
Connect both black and white LINE wires to the LINE TERMINALS on the new double pole thermostat. Connect both LOAD (heater) wires to the LOAD TERMINALS on the new thermostat. It will work correctly.
I have found a MEARS thermostat and found that the white wire is an optional antcipator and canbe connected to the load line thank for all the help
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Does everyone who wears full dentures use adhesive?
[ 5 Answers ]
I just started wearing full dentures in Jan. 07 after an accident. To keep my dentures from slipping and sliding I need to use adhesive on both uppers and lowers. My mother who is 90 doesn't use any adhesive and doesn't have any trouble? I'm not sure what the Norm is. Thanks to you all for any...
Is it normal that my husband wears girls underwear?
[ 12 Answers ]
I found a pair of underwear in my husbands closet when I confronted him about it he was mortified that he had to tell me they were his, is this normal for my husband to wear girls underwear because they are comfortable?
How long before deprovera wears off?
[ 1 Answers ]
I got a shot of this in dec of 06 I am going tfor another shot in April of 08 I have since then had sexual relations with others, is it possible that I couold in that time?:confused:
Is sex novelty that wears off?
[ 2 Answers ]
I'm a virgin. Me and my boyfriend plan on having sex sometime soon. It concerns me that he is a lot more sexual that I am. It doesn't really bother me (and because of this am I abnormal?) also I was just wondering once he startes getting sex from me, will the novelty like wear off. I'm worried that...
View more questions
Search
|