                |  | New Member |  | 
 
                  
                      Feb 7, 2009, 07:42 PM
                  
                 |  |  
  
    | 
        
        
        
       
        
        Luxaire burner won't start
       
                  
        My luxaire furnace won't fire up. When I open the bottom panel and flip the pressure swith over and over, it tries for about 1 second to run
     |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Heating & Air Conditioning Expert |  | 
 
                  
                      Feb 8, 2009, 05:58 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Exact model number of furnace?
     |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Feb 8, 2009, 09:54 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Mdl#  g8t11516uhc11as/n#   ekjm466306       when I flip the pressure switch on and off repeatedly, it tries to start up for a split second
 Thanks
 |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Ultra Member |  | 
 
                  
                      Feb 8, 2009, 10:18 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        I think you are referring to the interlock switch behind the blower access panel. The pressure switch is typically connected to the draft inducer via a small rubber hose. Sound right? Try this: Pull one of the wires off the PRESSURE SWITCH, then try to start the unit again. If it runs longer than before, the P/S is stuck in the closed position. Are there any status LED's on the unit?
     |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Feb 8, 2009, 03:57 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        I did mean the switch behind the access panel.
 When I flick it on and off, it sometimes tries to start for a split second
 |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Ultra Member |  | 
 
                  
                      Feb 8, 2009, 04:41 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        The interlock switch is interrupting and restoring the power supply when you disengage and engage it. Did you... try... my previous suggestion?
     |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Feb 8, 2009, 06:08 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        There is a red status light behind the access panel and the guide says if flash once then off then lockout caused by flame sensed... when there should be no flame
 |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Plumbing Expert |  | 
 
                  
                      Feb 8, 2009, 07:03 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Does the flame ever come on?
 |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Feb 8, 2009, 07:17 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        No flame ever
 |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Ultra Member |  | 
 
                  
                      Feb 9, 2009, 04:37 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Check flame sensor circuit for short to ground. Check circuit board for evidence of exposure to moisture (odixe trails, circuit path bridging).
     |  
    |  |  
 
 
 
  
    | Question Tools | Search this Question |  
    |  |  |  
 Add your answer here.
 
Check out some similar questions!
Burner motor won't stay on
 [ 1 Answers ]
Have a gas forced air furnace. Not sure of the name brand.   When it calls for heat, the burner kick on, but won't stay on.  They will burn for a short period, then they will turn off.  The fan motor stays running, but I had to turn the start temp for the fan way down so it would blow what warm air...
 
My Oil Burner won't start
 [ 1 Answers ]
Am. Standard Oil Burner just changed oil filter,nozzle.new tank and lines. Just had the unit serviced was running for a couple of days then shut off I bypassed the thermostat and it ran for the day however I couldn't get it started since. Could it be a flame out or defective Oil primary Control?...
 
Burner won't light
 [ 4 Answers ]
When I turn on the furnace the burner doesn't turn on what should I do?
 View more  questions
Search
 
 |