New Member
|
|
Feb 7, 2009, 11:26 AM
|
|
600 Amp 120/208V ,3Phase 4wire, Main Lug Only Service
Is there still a six throw rule in the NEC that would allow for a 600 Amp 3 Phase 4 Wire 120/208 Volt Main Lug Only Service or am I required to install a main breaker. The CT cabinet is a couple of feet away.
|
|
 |
Electrical & Lighting Expert
|
|
Feb 7, 2009, 11:59 AM
|
|
Sorry to be so blunt, but if you are an electrician installing a "600 Amp 3 Phase 4 Wire 120/208 Volt Main Lug Only Service" don't you think this is something you should know ahead of time and not have to come to a "Home & Garden" DIY board to ask about? Or at least ask this on a professional's site like Mike Holt's?
I know I'll get a negative comment on this one but I don't care. This is something I feel strongly about.
To answer your question though, yes, NEC 230.71 does apply. The panel you describe would be considered an MDP (main distribution panel), and can have up to six breakers/handles.
|
|
 |
New Member
|
|
Feb 7, 2009, 12:54 PM
|
|
 Originally Posted by stanfortyman
Sorry to be so blunt, but if you are an electrician installing a "600 Amp 3 Phase 4 Wire 120/208 Volt Main Lug Only Service" don't you think this is something you should know ahead of time and not have to come to a "Home & Garden" DIY board to ask about? Or at least ask this on a professional's site like Mike Holt's?
I know I'll get a negative comment on this one but I don't care. This is something I feel strongly about.
To answer your question though, yes, NEC 230.71 does apply. The panel you describe would be considered an MDP (main distribution panel), and can have up to six breakers/handles.
I take no offence to your "blunt" reply. I commend your interest in defending the quality of the people working in the industry. In response I must qualify that I have not worked in the design aspect of the industry in 25 years. I have held licences in 3 states and multiple city's. This question came up casually and having installed or supervised the installation of many services of this type in the past I questioned whether this was still a legal practice. Me, without a current code book in hand, was assisted by you. It would not be fair for you to receive flack for providing an honest answer. Thanks again.
|
|
 |
Electrical & Lighting Expert
|
|
Feb 7, 2009, 12:57 PM
|
|
Well then thank you very much for the professional response.
Good luck with your project. :)
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Running two 100 amp main panels from a 200 amp service
[ 27 Answers ]
Greetings!
I live in a rural country area. The electric company will be installing a pole, meter, and 200amp service with disconnect at pole. (It will require 50 foot run of service cable from pole to main load center in mobile).
Currently the double wide has a General Electric 100amp Main...
200 Amp Service Panel with 60 Amp Main Breakers
[ 26 Answers ]
I was told when we purchased our house that it had 200 Amp service which it appears to be; however, the top of each bus bars only has 60 Amp breakers for the Main shut offs. Is this normal? Each bus bar is connected to a hot wire (one red and one black) and then the two 60 amp breakers are...
200 amp main service panel
[ 1 Answers ]
I am planning on upgrading my main service panel (in basement) to a 200 amp service, I want to put a 100 amp sub-panel to the attic for central air and all the lighting on the second floor(about 18 hi-hats and 4 fans). From the 100 amp sub in attic I also want to run a 50 amp breaker feeding a...
Subpanel or main service panel?
[ 4 Answers ]
Hello,
I want to put a subpanel in my shop, and was wondering if a main service panel that they sell at say Home Depot is the same thing as a subpanel? I have a 200 amp service to my house, and want to put a 100 amp subpanel in my shop. Does the term "subpanel" just mean that it is wired off the...
Main Service Panel needs
[ 9 Answers ]
I ran across this site accidentally today and found someone who had many of the same issues I need help with. Most of my questions were answered reading the forum however I have one more, using the following information I am hoping someone can help.
The existing house is apx. 2300 sq ft w/a 200...
View more questions
Search
|