    Goodman won't light
    I have a 12 year old Goodman GMPN060-3 furnace. Occasionally it will not light the burners. Three technicians have come out to inspect it. The first person said it was the drain in the floor was plugged. He blew it out and the furnace worked for 2 weeks. Next tech came out and found the switch above the middle burner had tripped. Reset it and fine for 2 weeks. Third time the same switch had tripped. Switch is on order now. All 3 techs say that when the burners ignite, the flames are coming too far towards the access door. None of them can tell me why this is happening. There is central air installed in the furnace as well.
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #2

    Jan 9, 2009, 11:04 PM

    At the times its not lighting,, has you checked the circuit board for a blinking light (code),1 blink,, stop,, 2 blinks, stop, 3 blinks stop,, or what ever it might be,, if so look on the inside of the door and see what the code is,, did anyone check the gas pressure at the gas valve? Or
    reallybored's Avatar
    reallybored Posts: 4, Reputation: 1
    New Member
     
    #3

    Jan 10, 2009, 08:37 AM

    I have not checked for codes yet. Just found where the light was last night and will need to wait until it stops working again. As far as the gas pressure, I have not been here when they come but my wife says that the first tech did and it was OK
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #4

    Jan 10, 2009, 09:08 AM
    The switch above the burners? With purple wires? If so, that is a flame roll-out switch. If it is tripping, the area around it is overheating. This is usually the result of a leaky heat exchanger causing the burner flames to drift off target (hence the name flame roll-out). Try this: Observe operation from start-up. If the flames appear to be disturbed when the blower starts, you likely have a faulty primary heat exchanger.
    reallybored's Avatar
    reallybored Posts: 4, Reputation: 1
    New Member
     
    #5

    Jan 10, 2009, 09:17 PM

    Watched the flame while the blower started and it did not change. It is like there is a slight build up of gas when the igniter fires and a flash of flame backwards then everything runs fine.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Jan 11, 2009, 10:30 AM
    You have delayed ignition. Check for proper gas pressure and that the pressure matches the label on the furnace tag. Check to make sure all burner orfices are clean and if the burners are equipped with flame jumpers that they are clean.
    reallybored's Avatar
    reallybored Posts: 4, Reputation: 1
    New Member
     
    #7

    Feb 12, 2009, 08:32 PM

    Finally an update to my problem. After weeks of waiting to get the flame roll out switch replaced the tech showed up with the proper one. A couple of days earlier it had tripped and when my wife went to reset it it was hot although the furnace had been off for a while. The tech went to replace the switch and found it to be hot. After some further testing he found that the circuit board was faulty. Both the sensor and board have been replaced and hopefully after we return from a weekend away the furnace is still working.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #8

    Feb 12, 2009, 09:19 PM
    Glad you got it fixed. I hope it holds up for you.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Goodman gmnt-100 won't light [ 5 Answers ]

My goodman gmnt100 won't light just replaced the ignitor about 3 weeks ago was working fine and then started lighting intermittantly now won't go at all

Goodman furnace won't ignite [ 30 Answers ]

I have a 80% GMH8 goodman furnace that won't ignite. I can manually light it when the gas valve opens and it will run fine and shut off like normal. The glow plug ignitor doesn't come on but a couple of times I have saw it glow for a sec then go out way before the gas valve opens. The furnace was...

Goodman furnace won't stay lit [ 1 Answers ]

I have a goodman furnace that goes like this. Inducer fan comes on, 10 secs later glow lights up, 10 secs later get blue flames 10 secs later blue flames goes out. Repeats 3 times I have replaced the flame sensor still same problem But here is the thing. I am only getting 10 volts to the...

My furnace won't light and the lights on my control module won't come on [ 2 Answers ]

Ok a couple of question if you can help I have a comfortmaker furnace I believe 1999 it came on a couple of times after I bought a new transformer, board, capacitator, and ignition control module now it won't come back on What to Do! Also I wanted to know if you can tell me the difference between...

Goodman heating unit fan won't come on [ 1 Answers ]

The problem I have is the air handler is working but the fan on the compresser isn't going on. It's a Goodman unit... 2 ton I think... the unit comes on... the fan does not turn... but the unit makes a buzzing sound The unit is hot... in the time it took me to turn it on and walk outside and look...


View more questions Search