Ask Experts Questions for FREE Help !
Ask
    jimmyjosek's Avatar
    jimmyjosek Posts: 1, Reputation: 1
    New Member
     
    #1

    Jan 4, 2009, 05:24 AM
    3 Phase Fan on/off control
    I have an Exhaust fan with 3 phase (415v/50Hz) connection. How can I switch on & off this fan. I have a DDC controller with one relay output to control this fan. Which device I need, to connect my control to my Fan.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jan 4, 2009, 05:42 AM
    You can use a contactor or just a standard 3 phase disconnect depending upon how you want to control it. The site below is informative for DCC operation. Just make sure the contactor is aligned with the DCC control factors and if you want to get deluxe you can go variable speed. This actually needs to be calculated in the field using the original diagrams provided for the system so as not to cause interferences with the rest of the systems controllers or the main logic processor panel.
    MarkwithaK's Avatar
    MarkwithaK Posts: 955, Reputation: 107
    Senior Member
     
    #3

    Jan 4, 2009, 11:44 AM

    The easiest way I have seen would be a 3 phase disconnect, however if you want to be able to control this fan with a simple 115VAC switch then you could use a 3 phase motor starter with a 115VAC coil on the contactor. I would lean towards the motor starter as most have a phase protector to prevent the motor from single phasing in the even that you lose one leg of your 3 phase power. This is how I would, and have, installed 3 phase exhausts.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Option of 3 phase or single phase power, [ 2 Answers ]

How would one decide on which to use either 3 phase or single phase power to heat an airplane hanger?

How do you usually connect three single phase loads to a three phase generator? [ 2 Answers ]

How do you usually connect three single phase loads to a three phase electric generator?:)

How to go from 200Amps/208V/3 phase to 600Amps/480V/3 phase [ 2 Answers ]

I am starting a business and have equipment that requires 600Amps/480V/3 phase, but the site I want to rent has only 200Amps/208V/3 phase. Is there anything I can do to get the required power on that site? Any equipment I can buy to achieve this goal? I understand it may be costly. Thank you.

Detail explanation of eletrical between 3 phase and single phase [ 1 Answers ]

Hi, I do confuse between 3 phase and single phase,may I get some detail and comparison for each of them?

How am I going to size my 3 phase X'mer with 1 phase load using current as reference [ 3 Answers ]

Hi, I'm Peping: I have 90 pieces of single phase loads with current of 2 Amperes. This will be loaded to a 3 phase transformer, Wye connected having a line to line voltage of 220 Volts. What will be the size of the transformer required for the mentioned loads? Many thanks, Peping